old farmhouse boiler size
nogomomo
Member Posts: 6
Installing new boiler in farmhouse. Tore out old gravity feed 2 " lines, that have a circulator on now. 175k new yorker 30 yearold being removed. New windows, blowing insulation in most walls and adding r-19 to attic. 2300 square feet with 1 wall adjoining other half of house. Still will be an old farmhouse with some infiltration, installing condensing boiler, 10 degree outside, will 30 to 150 be too big, or 30 to 120 do the job? Baseboard cast iron first floor, cast iron uprights on 2nd floor
0
Comments
-
-
i was running a heat loss program and coming up in the 60k range, I could not imagine it would take one that big. the house did not have insulation on a lot of it at one time. thanks
0 -
Trust the math. Look for a boiler with a minimum firing rate under 20k. 15k would be even better.0
-
As has been said -- trust the math. First place, the old boiler may well have been oversized. It has happened... second place, if you blew insulation into the walls, you went from R4 (maybe!) to R10 or 12 for the walls. If you really got R19 in the attic, you went from R4 to R19. Both of these are big changes.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
second place, if you blew insulation into the walls..
___________________
OMAIR0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements