Head pressure
Techman
Member Posts: 2,144
Lets see here,it is around 0*F here in L.I.N.Y. and I'm headed out the door to work on an OUTDOOR R22 cond unit,medium temp case.Sitting here in my office, I'm going to take a S.W.A.G. at what the head pressure will be . So, what do u all think it SHOULD be? Come on now, be honest! I've told all of my workers that "I don't know" is an honest answer.I say "I don't know" many times a day, everyday.
0
Comments
-
Headmaster?
Fan Cycle?
Pump Down?
Low Ambient controls?0 -
All of the above.0
-
Should be 180 psi. Assuming the low pressure control settings are set to start the compressor at that cold of a temperature.0
-
All depends on how the head master is responding to the "0" temps. What really sucks is if the condenser is in a hi wind area, which will lo ball your head pressure head master or not. Considering perfect conditions,.....200 or so would make me happy.
MPT...0 -
95* condensing temp on a 70* day and 125* condensing temp on a 95* day. Most head masters are factory set for 90-95*( + or minus a little) cond temp. Some r404a cond units had an improperly factory installed head master that maintained a minimum pressuse of 180psig which is = to 82* cond temp and that produced an improperly operating TXV. By chance the TXV also requirers a minimum pressure in inorder to atomize the freon properly. The nitrogen charge in the head master will not be affected by any windy cold 0* day.0
-
Oh my! I do care ,because I work on the equipment as do lots of REFRIGERATION guys. R u a boiler guy?Who cares what the water feed valve press is or the temp of the water going into a radiant system.0
-
Talking Heat pumps??.......with head master and R404A !! LOL
You would be right about your feeling.0 -
You still want a 180- 200psig head no matter what temp is it out side.
If you don't have a high enough head pressure the TXV will never work right and it will not create enough pressure drop. I prefer head masters over fan cycling.0 -
Techman, I'd ignore what sludge says. I've watched/read a few of his replies on the forum, and it seems he's almost purposely trying to rile people up. Account was registered couple of days ago... Not sure what he's trying to do.Techman said:Oh my! I do care ,because I work on the equipment as do lots of REFRIGERATION guys. R u a boiler guy?Who cares what the water feed valve press is or the temp of the water going into a radiant system.
0 -
If you have a balanced port txv and properly sized liquid line you can get by with the lower head pressure but it's all got to be set up right. Liebert has a one piece valve for r22 that has a set point of 225 psi but most of the one piece oroa style valves come preset for 180. If we know that will be a problem we remove them and put on a ORI/ORD setup and then you get whatever you need.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements