Hi all. Fairly new to steam heat and have been having issues. Normally its my living room, which I may have fixed earlier. Seemed to be a pitch problem.
Now tonights issue is..normally the radiator in my bedroom is fine. Works great. Tonight it was a bit colder than normal and I have me new daughter in the house. So i turned the heat up a tad. To around 68. A few hours ago it was nice and warm in the bedroom. As the night went on it got cooler. I started checking things out.
Radiator is completely cool to about halfway down a vertical pipe in the first floor. From the boiler up to this point is nice and warm.
Any ideas why? Like I said. I normallly have no issues with this one. There is a mirror set up on the bed room next to the master bed and thats working fine. So was ruling out a pressure issue or something like that.
I just dont get what could be blocking it on a vertical run like that. Any help is much appreciated. Thanks.
Now tonights issue is..normally the radiator in my bedroom is fine. Works great. Tonight it was a bit colder than normal and I have me new daughter in the house. So i turned the heat up a tad. To around 68. A few hours ago it was nice and warm in the bedroom. As the night went on it got cooler. I started checking things out.
Radiator is completely cool to about halfway down a vertical pipe in the first floor. From the boiler up to this point is nice and warm.
Any ideas why? Like I said. I normallly have no issues with this one. There is a mirror set up on the bed room next to the master bed and thats working fine. So was ruling out a pressure issue or something like that.
I just dont get what could be blocking it on a vertical run like that. Any help is much appreciated. Thanks.
0
Comments
-
If the air can't get out the steam can't in, if this is1 pipe steam check the air vent.0
-
Also make sure no little hands have shut the radiator valve off.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Only little hands here are 3 days old. If she did it, frankly, id be impressed.
Here it is a few hours later and i just checked and the cold/hot mark has moved down closer to the boiler . Should I just change out the air valve?0 -
Changed the air vent and everything seems to be good. Thanks Mark.
Just thought it was odd that it was working fine around 7pm last night and then not at all a few hours later. Wouldve thought that was a progressive issue.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements