1968 Expansion tank replacement
eldridgehome
Member Posts: 2
I have an American Standard boiler, 4BN-J2, cica 1968. I would like to replace and relocate the expansion tank with a newer smaller model. How do I know how big of a tank (i.e. gallons) I need? Are there any issues concerning the replacement that I should be aware of? Thanks.
0
Comments
-
http://www.amtrol.com/support/extrol_com_sizing.html will help with the sizing. If the system has a lot of water (large diameter pipes) in it, use the commercial calculator. You can cross to a non-ASME tank with the same acceptance volume. You will also need to change your air control valve out for an air elimination device.
That boiler is well past its wear date. Have you considered a replacement?0 -
Thank you; it looks like I need the 4.4 gallon tank. I am not in a position to change out the boiler right now, but need to move the expansion tank, so a new smaller model looked like an inexpensive improvement.0
-