taco lwco
chrisdcmd
Member Posts: 2
i have a surge tank for a 75 psi boiler the pre fill tank is controlled by a series of lwco . the issue is they will randomly start flashing the red light meaning the control is bad. they can be reset and work fine. we have added a ground also cleaned probes made sure brass threads make good contact ,tested sensor . also the fill water is distilled which the water treatment guy says thats ok .
0
Comments
-
The blinking LED indicates the control failed an i ternal selftest. If the failure is the result of external noise from wiring and not because of a control failure, cycling power will reset the control as indicated in yoyr post. To trouble shoot this, we need information about the wiring configuration and connected equipment. Please contact me to discuss.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions1 -
the lwco are wired with 120v and hot jumpered too the common and back to the control panel which will close a relay and send 0-10vdc signal to a fill valve . there are 5 lwco's high limit cut out, cut in ,cut out, low level, low limit . they maintain water in a tank which feeds a pre heat tank then is pumped to the boiler . i can supply a wire diagram and pics if there is an avalable email1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements