Hi, I have a one pipe steam system that was banging away and spraying water through the vents etc. and after reading dans books i fixed the pitch of the pips sized the header right and it's all working fine, well almost no more water spraying but every so often when the system shuts off about a min later I hear a few bangs, it sounds like its in the wet return, any idea what can cause this banging?

Comments

  • Fred
    Fred Member Posts: 8,542
    edited January 2015
    Is that wet return a horizontal and is it above the Normal water level?
  • hi
    hi Member Posts: 31
    It's horizontal and it's on the floor the only part that comes up is the Hartford loop.
  • Fred
    Fred Member Posts: 8,542
    Is the Hartford loop above the normal water level of the boiler?
  • KC_Jones
    KC_Jones Member Posts: 5,796
    Also does it have a close nipple at it's connection to the tee?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • hi
    hi Member Posts: 31
    It's at the hight that the Manuel specifies, the only thing that I could think of is that the water level has bean jumping around when the boiler is working, could that have to do with it?
  • KC_Jones
    KC_Jones Member Posts: 5,796
    How much is the water level jumping around? Anything more than 1/2-3/4" is an indication you need to do some skimming to get oils out.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Fred
    Fred Member Posts: 8,542
    Yes, it sounds like you need to skim the boiler to get the oils out of it, possibly as a result of fixing the header, etc.That should stabalize the water in the boiler.
  • Jamie Hall
    Jamie Hall Member Posts: 24,531
    This can also be from thermal expansion (well, in this case, thermal contraction!), particularly if it just a couple of bangs.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hi
    hi Member Posts: 31
    Thanks for all your comments, I'll try skimming and see if that helps.