low water cut off

Options
teresad
teresad Member Posts: 4
is there a minumum suggested distance between the primary low water cut off and the manual reset lwco?
if too close and system surges have had some problems tripping manual reset. thaks

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Options
    LWCO distance of separation should not be a problem. What maybe happening is a spike in pressure from a faulty pressuretrol/pigtail could be pushing enough water out into the returns, causing a temporary low water condition. alternatively, the probe [or the water] may need cleaning.
    Install a low pressure gauge, on the same [newly cleaned] pigtail with them, keeping the useless 0-30 psi gauge, and verify your pressure.--NBC
  • KC_Jones
    KC_Jones Member Posts: 5,739
    Options
    Is this a new boiler? It could also need a good skimming if it's newer or has recently had work done. This can also cause the surging. I agree with NBC sounds like a surging problem not a LWCO problem.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control