Trying to resolve banging pipes

dkrz76
dkrz76 Member Posts: 6
Hi Folks -

New to the forum. Nightmare situation. Purchased an old home (built in 1935) in 2012 with a single pipe steam heating system. Loud banging upon start-up, in particular a radiator in the bathroom (near the bedroom of course). Had a new gas steam boiler installed in Oct 2013 by an incompetent plumber. Pipes still banged and boiler itself banged from time to time.

Had a new plumber in a couple of weeks ago. He told us the boiler was installed incorrectly - copper piping and incorrect piping in general. The old plumber didn't even follow the instruction manual. So we had this taken care of this week, plumber even signed a guarantee that the banging would stop. Within a few hours the banging came back. Plumber said he needs to come back to skim the boiler, as the boiler was never skimmed upon installation. He said the water was filthy and that should take care of the problem.

Could this be a factor? This guy seems really well informed in terms of steam heat. He's read Dan's book and calls it his "bible". He's attending numerous classes on the subject as well. But we've had such bad luck and have spent a ton of money trying to get this fixed that I thought I would seek a second opinion. And I just think it's strange that's it's mainly one radiator that's the problem.

Thanks!

Dave


Comments

  • dkrz76
    dkrz76 Member Posts: 6
    I appreciate the quick replies! Yes, he did install a skim port. I'll try to post pics tonight. The piping is totally different than how it was done before. We have already seen improvement as far as how fast the house heats, and the boiler itself is quieter. So I think we're on the right track. Testing our patience though.
  • BobC
    BobC Member Posts: 5,495
    Any steam pro is going to be busier than a one armed paper hanger at this time of year. He is waiting for all the oils to come down to the boiler so it can be skimmed, try to be there when he skims so you can learn how it's done because it often has to be done several times to get rid of all the oil.

    Bob.
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • JStar
    JStar Member Posts: 2,752
    I like that guy's attitude!

    You should ask him if it's okay to post his name and some of the piping pictures on this thread. We can always use more steam enthusiasts around here. Unless he's in NJ, then STAY AWAY! {/end sarcasm}
  • dkrz76
    dkrz76 Member Posts: 6
  • dkrz76
    dkrz76 Member Posts: 6
  • Fred
    Fred Member Posts: 8,542
    Looks like a nice install! Check tht radiator and it's supply piping for pitch as has been suggested and have the boiler skimmed (it may take 2 or 3 skims) and you should be good to go!
  • JStar
    JStar Member Posts: 2,752
    My only complaint is that both supply risers from the boiler need to be used. There is no way to eliminate one side without causing problems. The manual should state that rather clearly.
  • KC_Jones
    KC_Jones Member Posts: 5,796
    edited January 2015
    Not sure if this is that big of a deal, but it's not the "norm". The return pipes look like they are tied together above the water line which I thought wasn't supposed to be done?! Other than that it looks a whole lot better than most of what we see on here.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • dkrz76
    dkrz76 Member Posts: 6
    edited January 2015
    Thanks for the responses. I'm relieved it appears to be a good install, but I will mention the minor (hopefully) issues that were brought up.
  • Dave0176
    Dave0176 Member Posts: 1,178
    Could be wrong, but that boiler looks like a Dunkirk model, but branded different. If it is I know Dunkirk wants 2-1/2" risers out of the boiler, one or two, two being much better, into a minimum 2-1/2' header, and they specifically state [do not bush down the riser size]. I remember Steamhead saying these boilers are very sensitive to improper piping.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Fred
    Fred Member Posts: 8,542
    Dave0176 said:

    Could be wrong, but that boiler looks like a Dunkirk model, but branded different. If it is I know Dunkirk wants 2-1/2" risers out of the boiler, one or two, two being much better, into a minimum 2-1/2' header, and they specifically state [do not bush down the riser size]. I remember Steamhead saying these boilers are very sensitive to improper piping.

    It looks to me like a 2-1/2' riser with maybe even a 3' header. of course my eyes aren't what they use to be??
  • Dave0176
    Dave0176 Member Posts: 1,178
    edited January 2015
    Fred said:

    Dave0176 said:

    Could be wrong, but that boiler looks like a Dunkirk model, but branded different. If it is I know Dunkirk wants 2-1/2" risers out of the boiler, one or two, two being much better, into a minimum 2-1/2' header, and they specifically state [do not bush down the riser size]. I remember Steamhead saying these boilers are very sensitive to improper piping.

    It looks to me like a 2-1/2' riser with maybe even a 3' header. of course my eyes aren't what they use to be??
    Yeah pics are deceiving sometimes. Lol I do see all the bushings now. I know, it's the malleable fittings that are throwing me off!!!
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Gordo
    Gordo Member Posts: 857
    It looks to me like that installer is one of the good ones.
    Please have him come here and introduce himself!
    I bid him welcome.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • dkrz76
    dkrz76 Member Posts: 6
    An update. The plumber came back and skimmed the boiler. He also removed blocks that had been under the troublesome radiator in the bathroom. In addition, he insulated the pipe that leads up to the bathroom. It's only been a couple of hours but no banging! This guy really knows what he's doing. I never thought I would be able to find someone that could solve this problem!