Buderus 2017 on a gas boiler, term 12 needed?

GW
Member Posts: 4,593
Does anyone have an idea why the wiring directions show both line voltage and a switched leg going through the 2107? I have a guy calling us where the 12 term died. I fed the Honeywell with live power. The 10-11 are still switching the HW on and off heat call. I couldn't seem to get an answer for the Bud. Thanks, Gary
0
Comments
-
Terminal 12 is the manual reset high limit. The high voltage terminal (L1) of the aquastat must be fed from that.
Oil burners – factory jumper between terminals 12 & 10, brings 120V from 12 to 10. When contacts close between terminals 10 & 11, 120V power is sent from terminal 11 to Hot on the burner (terminal 4 is the neutral).
Gas burners – remove factory installed jumper between terminals 10 & 12. The contacts between terminals 10 & 11 are now “dry” (no voltage present) and switching to the burner is now low voltage between terminals 10 & 11 on the R2107 and TT (or RW) on the boiler aquastat.
Bob Boan
Bob BoanBob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Thanks Bob, the HW is the main boiler control, the 2107 is acting as a fuel savings device. I can see the point when the boiler control is removed (on an oil boiler). I'm simply trying to justify 'insisting' the home owner 'must' have a new 2107 installed.0
-
Gary,
The manual reset is under the black cap to the left of the temp dial.
There's also a fuse under the small cap to the right of the display.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
Categories
- 120.8K All Categories
- 83.8K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 416 Carbon Monoxide Awareness
- 36 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 116 Geothermal
- 154 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 754 Plumbing
- 5.3K Radiant Heating
- 358 Solar
- 13.9K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 37 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements