I'm doing a basement remodel and am looking to sanity check some work I am going to perform. In short, I want to remove all the iron pipe from the basement and run pex from a manifold to the different branches, connecting back to the old pipes where they leave the basement.
Boiler is an older Weil-McClain, 137K BTU. There is a single Taco circulator on the return side. When the boiler was installed (80s?), 1.5" copper was run from the boiler. On the supply side it connects to an ancient Thrush 120 flow control valve and then off to the iron. On the return side there are a couple of old Walworth thingies - not sure if they are to balance the flow? Pictures of the setup are attached.
The house has 13 radiators with a sum of 703 sq ft of radiation. Boiler seems to run around 170 degrees, which gives a radiation output of 105K BTUs (I realize the water temp can be adjusted up or down). I haven't done a heat loss on the house, which I realize should be done to get an accurate picture.
To the plumbing proposal. The 13 radiators are on 10 loops from the basement. Here is the load per loop:
Loop BTUs
1 7800
2 12000
3 12750
4 8550
5 9750
6 12600
7 22500
8 9450
9 6000
10 4050
I am planning to use a RiFeng manifold and 1/2" pex-al-pex. I like the manifold approach because I can then balance the loops centrally instead of dealing with frozen radiator valves all over the house. I'm looking at the RiFeng over alternatives such as a Watts mostly due to cost.
The 1/2 Pex-Al-Pex and the manifold ports should be provide enough flow for all loops except #7 (22.5K BTUs). This loop is a 1.5" iron pipe in the basement that rises to feed two radiators on the 2nd floor and one on the third. I can't split these to their own loop without tearing the house apart. To provide additional flow, I am considering creating loop 7a and 7b, with two 1/2" runs into a 1.5" tee at the pipe. (meaning 11 loops on the manifold). 5/8 pex would probably flow enough on a single loop but I'm not confident that manifold can flow enough on a single port.
My next concern is that the aggregate flow through the manifold would nee to be > 10 GPM. The manifold has 1" supply and return connections. Can 10 GPM get through that? Seems like it would be really pushing capacity. Therefore I am thinking of going with two 6-port manifolds instead of a single 12-port. I would tee off of the 1.5" copper on the boiler to a pair of 1" lines feeding the manifolds.
Finally, would an air separator, such as a taco vortech, make sense here? If I install this on the supply from the boiler to the manifold(s) would it eliminate the need to go around the house bleeding individual radiators?
Any thoughts, comments, suggestions?
Thanks,
Dave
Boiler is an older Weil-McClain, 137K BTU. There is a single Taco circulator on the return side. When the boiler was installed (80s?), 1.5" copper was run from the boiler. On the supply side it connects to an ancient Thrush 120 flow control valve and then off to the iron. On the return side there are a couple of old Walworth thingies - not sure if they are to balance the flow? Pictures of the setup are attached.
The house has 13 radiators with a sum of 703 sq ft of radiation. Boiler seems to run around 170 degrees, which gives a radiation output of 105K BTUs (I realize the water temp can be adjusted up or down). I haven't done a heat loss on the house, which I realize should be done to get an accurate picture.
To the plumbing proposal. The 13 radiators are on 10 loops from the basement. Here is the load per loop:
Loop BTUs
1 7800
2 12000
3 12750
4 8550
5 9750
6 12600
7 22500
8 9450
9 6000
10 4050
I am planning to use a RiFeng manifold and 1/2" pex-al-pex. I like the manifold approach because I can then balance the loops centrally instead of dealing with frozen radiator valves all over the house. I'm looking at the RiFeng over alternatives such as a Watts mostly due to cost.
The 1/2 Pex-Al-Pex and the manifold ports should be provide enough flow for all loops except #7 (22.5K BTUs). This loop is a 1.5" iron pipe in the basement that rises to feed two radiators on the 2nd floor and one on the third. I can't split these to their own loop without tearing the house apart. To provide additional flow, I am considering creating loop 7a and 7b, with two 1/2" runs into a 1.5" tee at the pipe. (meaning 11 loops on the manifold). 5/8 pex would probably flow enough on a single loop but I'm not confident that manifold can flow enough on a single port.
My next concern is that the aggregate flow through the manifold would nee to be > 10 GPM. The manifold has 1" supply and return connections. Can 10 GPM get through that? Seems like it would be really pushing capacity. Therefore I am thinking of going with two 6-port manifolds instead of a single 12-port. I would tee off of the 1.5" copper on the boiler to a pair of 1" lines feeding the manifolds.
Finally, would an air separator, such as a taco vortech, make sense here? If I install this on the supply from the boiler to the manifold(s) would it eliminate the need to go around the house bleeding individual radiators?
Any thoughts, comments, suggestions?
Thanks,
Dave
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 560 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
A couple of first observations:
1. I would not use any Chinese manifolds, particularly Rifeng. I've had a couple of jobs where customers supplied them and they leaked like sieves. Now, they get my manifolds or they get someone else. You get what you pay for. Look at Rehau, Caleffi, Roth, Uponor.
2. With 1/2" pex run from manifolds, most of the time you're not gonna get more than .75 gpm per loop, if that much. That translates to 7500 btu's at a 20* delta T. You'll need 5/8" or 3/4" for those rads requiring more.
3. Anytime you modify an old system, there are consequences that may not have been foreseen. If you're gonna err, do it by using larger runs. Maybe 5/8" minimum and 3/4" on the larger rads.
You can choose to do what you want, but you cannot choose the consequences.
You can see where I already ran some 1" pex to replace one of the loops (actually feeding a few off of that). I'm having balancing problems hence my desire to change the manifold.
I'll look into those other manifold brands.
Also, how many zones do you have? I'm assuming you have a single zone valve to the return on each manifold, rather than a value on each loop of the manifold. If that is the case, how are you balancing difference size radiators on the same manifold?