Zoning advice?

Hi,
This building is a community bath house, 4 full bathrooms roughly 9' x 9', utility/laundry room ~ 16' x 18'. All radiant, 1/2" PEX in 4" slab, 2" XPS under whole slab and perimeter. The two bathrooms in the front of the building have 2 exterior walls each, two in the middle have one exterior wall each. My calculated required slab temps for each of those three are 84.5, 83, 81 degF. (29, 26, 22 Btuh/ft^2 respectively at design).
Should I control these as separate zones w/ 3 thermostats? Or use 1 master thermostat for the building and try to balance flows on the manifold? If the latter, where should I put the thermostat? Would sensing the slab temperature be better than sensing air temp? (I'll definitely use PWM radiant thermostat(s), Tekmar or Wirsbo.) Please advise!
Thanks,
Jake
This building is a community bath house, 4 full bathrooms roughly 9' x 9', utility/laundry room ~ 16' x 18'. All radiant, 1/2" PEX in 4" slab, 2" XPS under whole slab and perimeter. The two bathrooms in the front of the building have 2 exterior walls each, two in the middle have one exterior wall each. My calculated required slab temps for each of those three are 84.5, 83, 81 degF. (29, 26, 22 Btuh/ft^2 respectively at design).
Should I control these as separate zones w/ 3 thermostats? Or use 1 master thermostat for the building and try to balance flows on the manifold? If the latter, where should I put the thermostat? Would sensing the slab temperature be better than sensing air temp? (I'll definitely use PWM radiant thermostat(s), Tekmar or Wirsbo.) Please advise!
Thanks,
Jake
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 563 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
Why not zone it, just an addition couple actuators and stats. Put a well into the slab for the sensors, pex with a copper stub on the end for good conduction, bring it right to the stats location.
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me
You can choose to do what you want, but you cannot choose the consequences.
Good question regarding the heat source, if you have a boiler will it also supply DHW? Sometimes a reverse indirect can buffer and produce DHW, Thermomax for example.
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me
I'm not sure how you calculated that... I get 2 rooms x 9' x 9' x 29Btuh/sf + 2 rooms x 9' x 9' x 26Btuh/sf + 1 room x 16' x 18' x 22Btuh/sf = 15246 Btu/h total load... (adding infiltration and downward loss and without rounding off my actual total is 16645 Btu/h)
The source is wood boiler with storage (GARN) so short cycling shouldn't be an issue. DHW will be a plate exchanger recirc loop to electric tank.
If I use a thermostat w/ slab sensor, wouldn't that not be able to respond to different heat loads at different times? I.e. the floor needs to be warmer to keep up in January than it does in September...so change the floor setpoint according to the season? Or does the tekmar consider both the floor & air temps in some smart way?
If you want to regulate slab temp to match the load, then you need variable speed injection mixing or a smart valve using outdoor reset. The Tekmar with the sensor will compensate some, but not to the degree that's needed to adjust slab temp to the load.
You can choose to do what you want, but you cannot choose the consequences.
The stat mention can impose limits on the slab and air temperature.
Remember whenever the slab surface is warmer than the ambient, heat energy is emitted. Roughly 2 btu/ square foot for every degree difference.
It all comes down to how much you want to $$ to have how much control. Indoor feedback, outdoor feedback, ODR, and even t-stats that tie to weather channels and adjust based on incoming weather, are all available currently.
I have had really good feedback from customers that use the combo air and slab stats. It is an affordable solution.
It's the unknown and ever changing load in an application like that making "exact" control a challenge.
I'm assuming there is a mix down device and the slab is not seeing 180°F from the Garn
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me
I found a good price on a Tekmar 509...that's the older model, now replaced by the 519. I can't find any info whether there's any significant difference between the two, any idea?
I used the 012 adapter plate also and mounted a 2X4 electrical box so the sensor well tube would end up in the box, behind the stat. That allowed you to insert and remove the sensor if it ever fails.
The adapter plate covers the electrical box perfectly.
trainer for Caleffi NA
The magic is in hydronics, and hydronics is in me