Munchkin boiler: P/S piping

Ross_24
Ross_24 Member Posts: 82
I've recently gained a new client with a Munchkin boiler. Installed in 2006. I'm partly concerned because the system is not piped primary/secondary. It is an old converted system with 3" mains running across the basement and cast iron radiators. Lots of water in this system.

Is this enough water mass to allow it operate correctly without P/S piping? Am I looking at flow problems that could cause an early demise for the HX? I would think a dirt separator and water treatment would be pretty key in this situation.

Pictures are shown below. Circulator is a Taco 0011









Comments

  • Ironman
    Ironman Member Posts: 7,512
    It's probably gonna get sufficient flow through the HX with those large pipes - assuming the circ is correct. On the flip side, the zones are probably over-pumped - particularly when one ZV is closed.

    I agree that some type of strainer/dirt separator should have been installed. I would do a thorough water and fire side cleaning of the HX before taking it under contract.

    Another note: over-pumping the rads can actually decrease their output. That may not be an issue since the house probably has a lower heat loss than it did originally due to window and insulation upgrades.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Ross_24
  • icesailor
    icesailor Member Posts: 7,265
    That 199M Munchkin is probably way oversized for your application. Especially with zone valves. It's lowest modulation level is still higher than what you might often see, and if the second zone is smaller and the only one running, it could be overheating from a lack of flow. Here is the Munchkin Installation manual. In NO drawing, do they show any boiler NOT piped Primary/Secondary.

    Does anyone ever read installation manuals and ask why things are described the way they are in there?
    There's a learning experience between the front page and back page in every one.

    http://www.htproducts.com/literature/lp-185.pdf
    Ross_24kcopp
  • Eastman
    Eastman Member Posts: 927
    @Ross P/S isn't some kind of dark magic. Just check the delta T across the boiler for individual zone calls at max fire.
    Ross_24
  • Ross_24
    Ross_24 Member Posts: 82
    icesailor said:

    That 199M Munchkin is probably way oversized for your application. Especially with zone valves. It's lowest modulation level is still higher than what you might often see, and if the second zone is smaller and the only one running, it could be overheating from a lack of flow. Here is the Munchkin Installation manual. In NO drawing, do they show any boiler NOT piped Primary/Secondary.

    Does anyone ever read installation manuals and ask why things are described the way they are in there?
    There's a learning experience between the front page and back page in every one.

    http://www.htproducts.com/literature/lp-185.pdf

    You're correct on that one my friend. It's at least twice the proper size.

    Good point. That's exactly what sparked my initial question. P/S examples only in the manual.
  • Ross_24
    Ross_24 Member Posts: 82
    Eastman said:

    @Ross P/S isn't some kind of dark magic. Just check the delta T across the boiler for individual zone calls at max fire.

    So I should take the magic wand out of my toolbox? :D
  • Eastman
    Eastman Member Posts: 927
    That would certainly make an interesting marketing angle for your clients.
  • icesailor
    icesailor Member Posts: 7,265
    As far as Magic, I saw a bumper sticker on a car with a lot of other stickers. Including ones in the shape of a fish.

    The sticker said: "God said it, I believe it, and that settles that".

    I think about that bumper sticker when I see something like that. Someone that does specific reading, not related to their job. And no other reading.
  • Ross_24
    Ross_24 Member Posts: 82
    edited December 2014
    So I'm back at the residence now. I had shut the make up water off overnight to gauge just what kind of state the distribution piping is in (it's an easy 100 yrs old) and this morning the boiler had a PR0 error (minimum pressure not met in the boiler).

    At first I thought no big surprise due to the age of the piping. There is most likely slow leaks all over the place.

    When I turned the make up water on and repressurized, the system went right back up and running. I did not have the purge anything and the radiators were back up and heating.

    It seems the minimum pressure issue was in the boiler solely. As soon as the make up water was turned on the boiler bounced right back to 15 psi.

    I may sound like a fool, but what kind of issue do you suppose I'm looking at here?

    Some quick facts about the situation:

    1. This customer is new to me.
    2. They had no heat for a period of 4 days prior to my arrival.
    3. A previous tech attempted to replace the expansion tank due to a dripping T&P valve. The expansion tank they used was much too small for the water volume and caused the system to over pressurize and blow down. They did not return and that's where I entered.
    4. I replaced with larger expansion tank and replaced the T&P Valve. System fired and maintained pressure.
    5. The boiler and near boiler piping is 7 years old. Distribution and emitters are easily 100 years old.
  • icesailor
    icesailor Member Posts: 7,265
    edited December 2014
    When it does what you describe, it usually means that there is no thermal expansion area in the system. Either a compression tank with no air, or a bladder type with the pre-charge wrong or the tank not working.

    If the system pressure through the Pressure reducing fill valve, is set higher or at exactly the same as the bladder tank, it will instantly go from zero pressure to what the fill valve adds. It can be as small as a teaspoon of water.

    Drop the pressure to 0# and check the pre charge pressure on the bladder tank with a tire gauge. It should not read zero.

    If the system is an old gravity system, you usually need a minimum of a #60 or equal bladder tank. Sometimes, two.
  • Ross_24
    Ross_24 Member Posts: 82
    edited December 2014
    icesailor said:

    When it does what you describe, it usually means that there is no thermal expansion area in the system. Either a compression tank with no air, or a bladder type with the pre-charge wrong or the tank not working.

    If the system pressure through the Pressure reducing fill valve, is set higher or at exactly the same as the bladder tank, it will instantly go from zero pressure to what the fill valve adds. It can be as small as a teaspoon of water.

    Drop the pressure to 0# and check the pre charge pressure on the bladder tank with a tire gauge. It should not read zero.

    If the system is an old gravity system, you usually need a minimum of a #60 or equal bladder tank. Sometimes, two.

    When I had left this morning it was fired up to temp and working again. I currently have a #60 and #30 exp tank, both new, on the system.

    I'll be back on site tomorrow morning with an HTP rep/trainer so I can learn more and see what he thinks about the current set up. Should be a fun day of learning.
  • icesailor
    icesailor Member Posts: 7,265
    Munchkins usually had a 10# minimum on their low pressure switch. Raise the system pressure to 14 or 16 #. It will keep it from cutting out if the pressure is too close.
  • Rich_49
    Rich_49 Member Posts: 2,769
    Easy and nice fix would be to add a properly sized circ for the boiler , throw a Caleffi Sep4 next to the boiler and change the circ on the system side to an ECM . This thing after a proper cleaning will work as intended by the manufacturer .
    Who is your rep and what trainer will be there with you ?
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    Ross_24
  • Ross_24
    Ross_24 Member Posts: 82
    edited December 2014
    Thanks @Rich could not agree more.

    Kevin Shea of Emerson Swan I believe.
  • icesailor
    icesailor Member Posts: 7,265
    The best nice easy fix would be to pipe it P/S like HTP wanted in the first place.
  • Rich_49
    Rich_49 Member Posts: 2,769
    Gee Ice , I pretty much thought that's what I just said . Of course simplifying it just a bit . A Sep4 is a hydraulic seperator
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    Gordy
  • icesailor
    icesailor Member Posts: 7,265
    edited December 2014
    Rich said:

    Gee Ice , I pretty much thought that's what I just said . Of course simplifying it just a bit . A Sep4 is a hydraulic seperator

    Sorry.

    I don't think in codes. I had no idea that a "Sep4" was a Califfi Hydraulic Separator.

    I personally think that everyone should use them when trying to go P/S. I did on every Veissmann boiler I ever did. Once I found out about them. They take any guess work out of tee spacing, and give a really nice chamber for the mixing to be done in.

    Some installers I met don't understand the concept.

    OBTW: My sister was born on Sep21.

  • Rich_49
    Rich_49 Member Posts: 2,769
    Why the mention of September 21 Ice ? Just curious why you would refernec such a date .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833