hot-water radiators on steam system
tomwc
Member Posts: 6
I have a steam system that the previous owner installed a hot-water loop for cast iron baseboard and toe-kick heaters on. Every time the hot water loop turns on (separate thermostat) the water level in the steam boiler drops and the boiler shuts down. I have read Don Holohan's discussion on piping a hot-water loop without a heat exchanger: the "water in the straw theory". The existing piping is not done as Don describes (not bypass line, and valves not in the right locations). I was going to have my plumber add piping to match the diagrams from Don, BUT THE QUESTION IS: I have 1/2" copper piping running to and from the boiler to the hot-water radiator loop - do I need 3/4" as Don illistrates, or will this system work with 1/2" copper piping? ANY help would be very appreciated. THANKS
0
Comments
-
Sounds like the loop could be draining when the pump shuts off?
1/2" is pretty small. How many BTUs does the zone need? What are the supply and return temps when it's operating?0 -
Yes, the loop drains when the circulator stops.
I'm guessing that the zones need between 40-46,000Btu's. Not sure of the temperatures of the supply & returns. The supply piping is currently off the 'mud' leg of the boiler.0 -
46k at a 20˚F ΔT is 4.6 GPM. 1/2" pipe is not big enough.0
-
The 1/2" piping is what I'm stuck with, in the existing construction. If I figure 20 deg. delta, then I'm down to +/19K. Will the 1/2" piping hold the water in the piping under atmospheric pressure, so it does not drain down into the boiler when the circulator stops?0
-
Is this a series loop? Any chance you can split the loop?
I need to defer to one of our steam experts on the water level question.0 -
-
Can you break into the loop somewhere in the middle and run a 3/4" line back to the boiler?0
-
In order to make it 2 loops, and install another circulator?0
-
THANKS0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements