the most frequently asked question?
plumb12
Member Posts: 3
in Gas Heating
The most frequently asked question Circ's or ZV's?
With massachusetts rebates, variable speed pumps equal the cost of ZV's now.
Senario #1) A FHW boiler P/S loop, single delta T circ with a multiple ZV system will have each circuit balanced.
Scenario #2) Same as above, except with multiple delta T circ's.
Which method is more effective and efficient on a multi zoned system?
With massachusetts rebates, variable speed pumps equal the cost of ZV's now.
Senario #1) A FHW boiler P/S loop, single delta T circ with a multiple ZV system will have each circuit balanced.
Scenario #2) Same as above, except with multiple delta T circ's.
Which method is more effective and efficient on a multi zoned system?
0
Comments
-
-
Yes, this is a residential application. I'm not referring to high head pumps for multi-residential or commercial heating pump systems with VFD controllers. A home with about 3000SF heating area and six zones ranging from 1-4 gpm0
-
-
-
-
ZV's & a Delta T circ large enough for the total maximum GPMYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331 -
you gotta do the math. in order to pick the right circ, you need to know the flow (Universal Hydronics Formula) and then you need to know the head loss of the project.
Otherwise, you are just guessing and hoping it will work. Will it work with just choosing one over the other? Probably. But what if it doesn't. Whose to blame?
With the controls on the circs, you need to make sure the correct control strategy is chosen. When it doesn't work because the math wasn't done, the component gets the blame and its less feature-rich brother gets installed.
Make sure you know what you have in your hand and why you are using it for your customer. What reasons do you have for zone valves over circs? Go with what works and what you feel comfortable with. All of these pumps can easily do alot of house by themselves.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
1 -
Good point, Dave.
Circulators have efficiency curves as well as performance curves. Peak efficiency typically occurs very close to their rated RPM and that when running slower, their hydraulic efficiency is reduced. Running an ECM circ at the bottom of its range gives it no room to modulate.
Just because your (circulator, boiler, furnace -- pick one) modulates does not mean you can ignore sizing.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements