Gas valve

jerrmorejerrmore Posts: 1Member
I have a heater that has a Honeywell SV9520H8034 gas valve. The signal is 6 and 1. Is the valve bad?

Comments

  • Tim McElwainTim McElwain Posts: 4,278Member
    6 flashes plus 1 indicates Soft Lockout condition maximum retry count was exceeded - 4 trials for ignition in the call for heat. Check the following:
    - 1. Gas supply off or the gas pressure is too low to operate the appliance
    - 2. Damaged or broken HSI element
    - 3. Appliance is not properly grounded
    - 4. Flame sense rod needs cleaned or is grounded to the appliance chassis or is out of position
    - 5. HSI element and flame sense rod wiring not making a good connection.

    None of these indicate anything is wrong with your gas valve.