primary secondary question
The home is 1300 sq ft home currently using an oil fired boiler with cast iron radiators on a single zone.
I will be replacing with a gas fired cast iron boiler and will be splitting off 2 bedrooms to its own zone and adding an indirect water heater, so, there will be a total of 3 zone run off of the new boiler.
I read Dans book, "pumping away" and found it incredibly educating. I wish i had it 25 years ago as i found explanations for issues i had back in my service days.
Anyway, is there any reason i cant use zone valves fed by a single circulator on the secondary circuit instead of circulators on each zone?
Comments
-
not sure you need primary/ secondary? Unless you want multiple temperatures or have pumping conflicts with high pressure drop heat exchanger type boiler.
I do like to see boiler return protection on high mass or large water content systems, it assures the boiler always reaches a good operating condition.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
There's no reason you can't use zones valves as long as the smallest zone isn't over- pumped and all zones combined aren't under-pumped. I would use a Delta P pump like the Grundfos Alpha or Wilo Stratos if you use ZVs.ffp20 said:In a previous life i was a service technician for an oil company many years ago and now i find myself replacing a boiler in one of my homes.
The home is 1300 sq ft home currently using an oil fired boiler with cast iron radiators on a single zone.
I will be replacing with a gas fired cast iron boiler and will be splitting off 2 bedrooms to its own zone and adding an indirect water heater, so, there will be a total of 3 zone run off of the new boiler.
I read Dans book, "pumping away" and found it incredibly educating. I wish i had it 25 years ago as i found explanations for issues i had back in my service days.
Anyway, is there any reason i cant use zone valves fed by a single circulator on the secondary circuit instead of circulators on each zone?
I agree with HotRod about p/s and return temp protection.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
What kind of emitters are installed? Have you done a room-by-room heat loss calculation?0
-
SWEI i have done the calculations. The rooms have cast iron radiators.
Hotrod i thought of using primary/secondary because of return preotection. As i said the house has cast iron radiators with a short 2" reduced to 1-1/2" mains. Would a bypass suffice then and not do primary/secondary?0 -
What water temp will you need on a design day to satisfy the load?
With CI rads, I would look seriously at a fire-tube mod/con boiler. By the time you add a motorized mixing valve with ODR control, a second circulator, and the additional pipe and labor the cost will be very close. The mod/con will take up less space and give you additional control capabilities.3 -
Hello gentalmen , I will be replacing a similar system , currently I have 1 zone hydronic system with 2" supply and return lines they out the basement in a 3 family home, I wanted to slightly over size the boiler to make up for the volume of water in these pipes and it has big cast iron rads,, it will be a oil to gas conversion as well. I will keep the oringnal zone, had a additional new loop zone on 1st floor and also add a super store storage tank, so a total of 3 zones, I was thinking about doing primary secondary pumping on this project , the question I have is , SHOULD I pipe in the domestic tank before the primary pump to help the tank keep up at high demand? Or pipe it out on the secondary pumping like the other 2 zones, and no the owner does not want a condensing boiler lol, thank you, bmtcorp@aim.com0
-
Elvir , You may want to start a new discussion .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements