Should I replace my oil tank?
scott_homeowner
Member Posts: 5
Contractors have given me conflicting information about my Cardinal 275 gal tank - installed in my basement in 1970. Does the rust on the bottom indicate it is time to replace this tank or is that rust superficial and not an indication of a problem? Given the age of the tank, do I go ahead and replace it anyway? (Photos are linked above.)
0
Comments
-
Thank you Jamie and bc3510 for your input!0
-
The only really positive way to find out if a tank is rusted to the point it needs replacement -- other than the slow drip from a pinhole, which is a pretty good sign -- is ultrasonic thickness gauging to the metal. And for a tank like yours, it isn't worth the very considerable cost. They almost always rust out from the inside, not the outside.
Can't guarantee anything from how it looks on the outside -- but I must say yours doesn't look bad at all.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England5 -
At 45 years old I would start considering replacement-for peace of mind\reliability/safety-a tank that old is bound to have sludge on bottom and nasty bugs that nibble on the metal. You don't want to wait until a pinhole happens. Oil lines deteriorate too.5
-
Bob, We may opt for the "peace-of-mind" strategy.0
-
scott..don't forget..the fuel line going to the oil burner is a few inches higher from the bottom of the tank. we all try to listen to the old timers and the information left by the dead men.
I was told by an old timer that once you start with cleaning and messing with the sludge on the bottom of the tank you could cause trouble and leaks.
I was thinking about doing that but didn't. i put in some of that antisludge once in awhile, turn off the ball valve and emergency switch for an hour or so when oil is being delivered.
i tune up the boiler myself, vacuum it out and monitor it as well.
when you put a new tank in the sludge will be on the bottom below the pipe as well unless they changed that. I sealed all the piping with the good blue sealant and all is fine. Put an inline filter as well and ball valve on the oil tank. i changed all the copper lines and fittings as well.
you can also change the way the pump is set up with a two pipe system so you won't have to bleed it and have much of a sludge problem.
I basically take care of the boiler and burner like an engine in a car.
you will have to take in all the information and based on what you think will do what you feel is right. don't forget if ihave problems at midnight i don't call anyone else in..and take care of things myself.
i personally just change parts when they are broken or i feel they are on the way out...that's just the way it is with me. if i have to change my oil tank at some point..i'll make sure who makes the tank, what material it's made of,etc,etc..
looking at the photos most just look like surface rust...maybe from water dripping or something too.. i see the bottom pan under there...is this leaking and if so from where?
it seems if this tank were rusted through there would be leaks all over the place.
good luck in whatever decision you make.0 -
Ww, if I may I just correct a couple of things in your otherwise great post?
Never ever would it be good to pump over oil from an old tank to a new one-the bacteria/algea in the old oil would make a premature sludge factory. Out with the old, in with the new!
2 line systems make a sludge problem WORSE for filters etc. bc the pump flows it's full capacity thru them. Then there's the return line environmental hazard if it should leak. Not desirable. The solution is an oil deaerator that would accomplish self bleeding and overcome lift or high pull scenarios. I even use them on 1 pipe gravity fed jobs for convenience at times. The Tiger Loop Ultra with it's spin on filter is my go-to.
My preference for above ground steel tank delivery piping is one pipe, off the bottom of the tank, tank pitched to the outlet, whenever possible to minimize build up in the tank.1 -
The tank is 44 years old. Are you still driving a 44 YO car on a daily basis? If and when the tank starts to leak, it will not start leaking like you pulled the pop-top on a can of beer. It will get a "pimple" of rust near the bottom and if you want to poke at it, you will probably start a leak.
Someone "modernized" the tank with the new vent, whistle and gauge. And the new bottom outlet fitting. There's still a ton of sludge inside the tank. There appears to be a couple of "pimples" on the bottom of the tank in the photos. Don't be a teenager and pick them. They might bleed.
No one is trying to get access to your wallet by suggesting that you need a new tank. But if you are going to be there and not be switching from oil, a new Roth or Shute type tank would be nice with a Tigerloop on the burner and one pipe to suck out of the top of the tank. Let the sludge collect on the bottom and you won't be dealing with the sludge in the oil feed line.
I've seen them a whole lot older and not be leaking. If they develop "Pimples", they don't start leaking right away. I see far more start weeping on seams than I do leaking in just the tank part.
If you decide to try to sell the house, or need some home inspection for insurance purposes, the first thing they are going to pick at will be that oil tank. Inspectors and insurance companies look at old oil tanks like a potential Ebola epidemic.
If you decide to change the tank, run it down to the bottom, then change it. Don't get it changed when it is full. Some oil tank removal service will charge up Vaseline prices to transfer the fuel for waste purposes into their own tanks, filter the heck out of it and get "free" fuel, that you paid them to have removed.
Sort of like Excavation Contractors who dig a hole and charge to take the dirt away. They, they drop it off somewhere else as fill and charge the person that gets your fill. Then, because they took away too much fill, you need replacement dirt so they charge you full bore for new fill. Sometimes, fill that they stored in their yard for others. In other words, they get you coming and going.5 -
We currently have 1/2 a tank of oil and we were encouraged to have that oil pumped out of the old tank and back into the new tank. Thanks Bob for suggesting that isn't the best way to go. Some of you are recommending Tigerloops. None of the local service guys have mentioned this. I get that it addresses air in the fuel line; what's not clear is why I need this if the burner functions without it. (I have a System 2000 boiler.)0
-
Hi Scott, burn up that old oil, don't transfer! No one can say precisely where the "good" stuff ends and where the junk starts Start fresh with new oil. Plan the changeout related to your usage. Worse case the oil co can put you on 5 gall cans while the swap happens.
Tiger Loops can be exotic for some outfits- but they've been around a long time. It's a sure way the burner gets solid oil to burn clean, they prime the pump and are convenient for service, and the Ultra model has a top shelf car type spin on filter built into it.
The Loop will ensure your EK is getting the cleanest and best oil supply. The burner may run now, but is it running to it's best efficiency?0 -
How were you filling the Garber? Something doesn't sound right.
Running 2 line thru oil filters does NOT clean a tank, I can assure you of that.
We are striving to not have to change filters 2x a year here.
You want to run a single line top feed direct to burner, it can be fraught with issues.
Completely disagree with the statement that bottom feed is not the best solution. Pitch the tank, reduce sludge build up.1 -
Really BC? You go right ahead and dump that old oil into a new tank. Customers will really love that and will be amazed at what you deem "acceptable" color oil to be viable vs what isn't. Give me a break.
That Tiger Loop "contraption" is standard equipment on Buderus Blue Flame units. Why do you suppose that is? To jack up the price of an unjustifiable costly boiler in your eyes?
Nice way to bash trade practices/people.0 -
Replace the tank, bottom fed, and pitched towards the supply line per code. No need for Tiger Loops, and more important no 2 pipe, as Bob is dead on with high vacuum, and trying to filter all the oil, and crapping up the filter/strainer for no good reason. Also key, run a new sleeved supply line, and still put an additive in first fill up. Transfered oil or not, the inside of a new steel tank has been coated with oil that helps prevent rusting until filled for the first time. That will liquify
0 -
Again, I will do a TL on a gravity fed just for the convenience, and the filter setup on it, on occasion. Mounted at the burner location where it should be.
And the answer to the Buderus question is that they want the cleanest, most airfree oil at the lowest Hg for high burner performance. Those proprietary burners can see 350 pump pressure plus. Oil "stretch" is not acceptable.
4-5 years a certified Buderus BF contractor here.0 -
BC. You prefer top fed lines. Do you drain the sludge/condensation from the bottom outlet, or do you wait until there is a foot of crap in the bottom of a tank?0
-
Sure, the potential for clogging at the tank valve can occur. But I would much rather that then a level or back pitched tank holding nasties and etc that will eat the tank much faster. If there's getting to be plugged up tank valves, it's time for at minimum some feel good tank treatment or tank replacement. Nothing lasts forever.
The oil industry is not in good shape. Who wants to deal with no go's from post delivery sludge ups, fuel quality issues leading to soot ups, problematic delivery to the burners etc, noise, smell...
Gas looks real good....
We need timely replacements, and to take advantage of products that exist to make these things as troublefree as possible0 -
But 2 pipe won't clean a tank. That was never the intention of the design. The return piping is subjected to pitting and erosion by the fuel and that "reaction" gets carried back to the tank. The return dumps the oil back into the tank, further stirring and agitating the algea bugs.
Sludge is gonna win no matter what.0 -
Pitting and erosion of the copper lines will happen regardless 1 or 2 pipe and where the filter is.. All you can do is protect the burner components. One can put a filter at the tank, even do a "sludge pot", but from there to the appliance it's still fuel deterioration.
Again, the better of the scenarios is to pitch the tank to a bottom outlet to try to extend the tank life.0 -
Bob Bona said:
Sure, the potential for clogging at the tank valve can occur. But I would much rather that then a level or back pitched tank holding nasties and etc that will eat the tank much faster. If there's getting to be plugged up tank valves, it's time for at minimum some feel good tank treatment or tank replacement. Nothing lasts forever.
The oil industry is not in good shape. Who wants to deal with no go's from post delivery sludge ups, fuel quality issues leading to soot ups, problematic delivery to the burners etc, noise, smell...
Gas looks real good....
Most people would switch to gas- either natural or propane, so for them none of this is an issue.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
That's not the whole picture- besides the aforementioned tank issues, there's inconsistent delivery, poor maintenance (if any maintenance at all) odors, puffbacks- the list goes on.
People switch to propane because it isn't oil.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
ok great bob..i have a one pipe but figured would put that in since i read that it was an option and works in other cases...will do more reading on the subject...
i was interested in that since it said in my readings that you wouldn't have to prime the pump again and you will have no sludge..as far as putting the old oil in the tank..that's not what i meant..i meant that if you put a new tank in eventually the sludge will be below the pipe anyway.0 -
The TL is an upgrade to any system. Some require it due to difficult piping configurations, others, it's an enhancement. And having the spin on filter as part of the unit is sweet.0
-
Where are you located Scott? A couple of things here. First is The fill should not be larger in diameter than the vent pipe. Code here in Mass, maybe not where you are, but common sense just the same. Next is I hope the new tank will not have that shameful one piece valve under the tank. These are an accident waiting to happen. Have them go iron fittings, out to a positive shut off, an inline thermal valve, filter, and all flared fitting with a protected/sleeved oil line. I would also have all new piping and a new screened vent cap outside. Just some food for thought0
-
-
-
What a show.
A Tigerloop at the burner with a spin on filter into the Tigerloop, and a spin on filter at the tank, gets rid of all the sludge issues. The pump strainer and nozzle never get dirty and can go for years. When you service the burner, there is usually a valve at the tank before the filter. A container under the filter with the filter removed, and the valve opened until the sludgies leave and the oil runs clear is a good way to get rid of sludge in the tank.
When you return to the tank, you just run the oil around, expose it to air, and allow aerobic bacteria to grow and feed on the oxygen in the oil. Kind of like an aerator in an aquarium.
A Tigerloop is just a 2 pipe oil system. Required in many countries in Europe. Like a lot of things that work well over there. Some feel that the USA is a different part of the universe with different laws of physics.2 -
I don't know how old my tank was but when we pulled it out of the crawl space it certainly didn't look new.
All it had on it was a UL number with "Underwriters laboratories" spelled out in script which to me screamed 1940s. No leaks or anything. I was told it previously didn't have a vent and that was added sometime in the 2000s along with the whistle. It had a valve on the bottom which had it's copper tube crimped off and then a modern single pipe top feed installed.
This info may or may not help you, but I figured it couldn't hurt. If it was mine, and in my basement I would likely have it changed if I had any doubt. I know little to nothing about oil tanks or how often they rott out but what I do know is I highly doubt it waits until a convenient time to do it.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
That tank is late 50's, early 60's
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements