Gravity hot water diverting tee
Dave_132
Member Posts: 65
Does anyone know if this will work with forced circulation ? It is in a 100 year old home and we are changing the boiler. I think that it had an internal diverting casting to send water up on the right and pick up the return on the left. I hope that we wouldn't have to disturb it.
There was an error rendering this rich post.
0
Comments
-
Don't think it will work
I believe it relies on the different temp layers within the large mains. It does not "scoop" the water like a more modern diverter tee. I believe it was called stratification? You will probably be adding return mains.0 -
Pump?
I know close to nothing about hot water heat and am asking this just for my own knowledge.
Why convert a gravity system over to forced? If it's worked for 100 years why add a pump now being all of the piping is already in place?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Hot Water
Agreed that you might have trouble adding a pump to this system. I would keep it as gravity. What kind of boiler are you installing? I would use a mod/con feeding a large buffer tank or hydraulic separator with only one pump for the boiler. The storage tank will act like a gravity-feed boiler.0 -
Eureka Tee
It's a Eureka Tee.
There's a thread on the wall a couple of notches down that's discussing this titled : Old house, diverter Tees.
http://www.heatinghelp.com/forum-thread/151329/Old-House-Single-pipe-hydronic-with-diverter-tees
JStars advice about using a buffer tank is good. It's the best solution that we came up with, too.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
It should work fine with a circ
as long as the circ is properly sized to mimic the gravity flow. Size your circ from the chart in this article and you should be fine:
http://www.heatinghelp.com/article/343/Circulators/238/Sizing-Circulators-for-Hot-Water-Heating-SystemsAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Agreed...
If using a cast iron boiler which has little or no head. But a mod/con which usually has high head and needs high velocity is gonna need hydraulic separation to work with this type of system.
Remember, it's not just a gravity system; it's a system that requires stratification in the piping to function.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Cast iron boiler
I plan to use a cast iron boiler with a very low gpm pump and low head. The buffer tank is a good idea however we have space limitations . What is available that would match the old gravity flow and allow the hot water to migrate similar to the old system.
Has anyone ever been able to determine the flow rate on a gravity system.There was an error rendering this rich post.
0 -
Your
system is not a conventional gravity system. Yours is a one-pipe system. If you could pump it slow enough to ensure the stratification within the main, there would be no advantage to doing so.0 -
How many square feet
of radiation do you have?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Square feet of radiation
I will be measuring all the heat radiators tomorrow in order to determine total amount.There was an error rendering this rich post.
0 -
ChrisJ
Control is the reason Chris. 100 years ago Fuel was cheap if it got to hot you just opened a window. Today you open a window its like opening your wallet. No one complains only if there is not enough heat.0 -
Flow Rate
The flow rate will vary depending upon the water temp. As it gets hotter, it will increase.
If you measure the Delta T between supply and return, and you also know the btu output of the boiler, then you can use the universal hydronic formula to find the gpm.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Speeding Pumps:
Multi-Speed and Variable Rate circulator pumps can be a wonderful thing.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements