Gravity hot water diverting tee
Dave_132
Dave_132 Member Posts: 65
Does anyone know if this will work with forced circulation ? It is in a 100 year old home and we are changing the boiler. I think that it had an internal diverting casting to send water up on the right and pick up the return on the left. I hope that we wouldn't have to disturb it.
  • Paul48
    Paul48 Member Posts: 4,469
    Don't think it will work
    I believe it relies on the different temp layers within the large mains. It does not "scoop" the water like a more modern diverter tee. I believe it was called stratification? You will probably be adding return mains.
  • ChrisJ
    ChrisJ Member Posts: 17,257
    Pump?
    I know close to nothing about hot water heat and am asking this just for my own knowledge.
    Why convert a gravity system over to forced? If it's worked for 100 years why add a pump now being all of the piping is already in place?
  • JStar
    JStar Member Posts: 2,752
    Hot Water
    Agreed that you might have trouble adding a pump to this system. I would keep it as gravity. What kind of boiler are you installing? I would use a mod/con feeding a large buffer tank or hydraulic separator with only one pump for the boiler. The storage tank will act like a gravity-feed boiler.
  • Ironman
    Ironman Member Posts: 7,898
    edited September 2014
    Eureka Tee
    It's a Eureka Tee.
    There's a thread on the wall a couple of notches down that's discussing this titled : Old house, diverter Tees.
    http://www.heatinghelp.com/forum-thread/151329/Old-House-Single-pipe-hydronic-with-diverter-tees
    JStars advice about using a buffer tank is good. It's the best solution that we came up with, too.
    Bob Boan
    Steamhead Member Posts: 18,368
    It should work fine with a circ
    as long as the circ is properly sized to mimic the gravity flow. Size your circ from the chart in this article and you should be fine:
    http://www.heatinghelp.com/article/343/Circulators/238/Sizing-Circulators-for-Hot-Water-Heating-Systems
    Consulting
  • Ironman
    Agreed...
    If using a cast iron boiler which has little or no head. But a mod/con which usually has high head and needs high velocity is gonna need hydraulic separation to work with this type of system.
    Remember, it's not just a gravity system; it's a system that requires stratification in the piping to function.
    Bob Boan
  • Dave_132
    Cast iron boiler
    I plan to use a cast iron boiler with a very low gpm pump and low head. The buffer tank is a good idea however we have space limitations . What is available that would match the old gravity flow and allow the hot water to migrate similar to the old system.
    Has anyone ever been able to determine the flow rate on a gravity system.
  • Paul48
    Your
    system is not a conventional gravity system. Yours is a one-pipe system. If you could pump it slow enough to ensure the stratification within the main, there would be no advantage to doing so.
    How many square feet
    of radiation do you have?
    Consulting
  • Dave_132
    Square feet of radiation
    I will be measuring all the heat radiators tomorrow in order to determine total amount.
  • Gordy
    Gordy Member Posts: 9,546
    ChrisJ
    Control is the reason Chris. 100 years ago Fuel was cheap if it got to hot you just opened a window. Today you open a window its like opening your wallet. No one complains only if there is not enough heat.
  • Ironman
    Flow Rate
    The flow rate will vary depending upon the water temp. As it gets hotter, it will increase.
    If you measure the Delta T between supply and return, and you also know the btu output of the boiler, then you can use the universal hydronic formula to find the gpm.
    Bob Boan
  • icesailor
    icesailor Member Posts: 7,260
    Speeding Pumps:
    Multi-Speed and Variable Rate circulator pumps can be a wonderful thing.