Boiler Room Configuration
tejay
Member Posts: 1
I'm designing a mechanical room for a radiant floor system. 3700 sq ft home retrofit. I've mostly settled in on the design below, but wanted to get it sanity checked by some folks with more experience than I have. There is a full diagram attached. As always, thanks for sharing your knowledge and experience with the group. We genuinely appreciate it.
Assumptions/Facts:
<ol><li>48k BTU heat loss</li><li>15 Degree Delta T</li><li>105 Degree Supply Temp</li><li>20K BTU "Backloss"</li><li>6 Zones (5k - 10k BTU each)</li><li>All zones are 2-2.5 ft of head</li><li>Polaris water heater hacked to supply 140-155 water</li></ol>
Components
<ol><li>Polaris 130K 34 Gal</li><li>Sentry zone valves</li><li>Alpha system pump (on constant pressure) </li><li>Bumblebee on heat exchanger loop (at 105 setpoint, manually adjusted for outdoor temp)</li></ol>
Questions
<ul><li>Given that the system should always be pushing more flow than the heat exchanger loop, am I right to have the system as primary and the heat exchanger as secondary? Or should they be switched?</li><li>I could use a taco 007-vr on the polaris side, and loose the bumblebee and secondary loop all-together, but the VR is 3X the cost of the bumblebee. Is the added complexity penny wise and pound foolish? Is there a cheaper circulator that does setpoint variable speed and is brass/stainless?</li><li>I've got both the alpha and bumblebee oriented vertically. That adds a few bends to the system, but it's my understanding it will help ensure air bubbles travel toward the air eliminator. But with both pumps pulling water downhill (and thus pulling air bubbles down too) does it really help anything?</li><li>Are there any other obvious flaws here that are making me look stupid (I've got thick skin, I can take it).</li><li>What should be done about backloss? My understanding is that some of that heat is truly lost, but that much of it is coming right back at you in the form of thermal mass. Is there a rule of thump for how much you get back? I've got slab, crawl space, and second story all in the mix, if that helps any.</li><li>Polaris is available in 34 and 55 gal models. Without the hack, either model will cycle like crazy, taking less than a minute to overcome the 3 degree delta built into the system. With the hack in place, is the extra energy storage of the 55 Gal model worth the extra cost and space?</li></ul>
Assumptions/Facts:
<ol><li>48k BTU heat loss</li><li>15 Degree Delta T</li><li>105 Degree Supply Temp</li><li>20K BTU "Backloss"</li><li>6 Zones (5k - 10k BTU each)</li><li>All zones are 2-2.5 ft of head</li><li>Polaris water heater hacked to supply 140-155 water</li></ol>
Components
<ol><li>Polaris 130K 34 Gal</li><li>Sentry zone valves</li><li>Alpha system pump (on constant pressure) </li><li>Bumblebee on heat exchanger loop (at 105 setpoint, manually adjusted for outdoor temp)</li></ol>
Questions
<ul><li>Given that the system should always be pushing more flow than the heat exchanger loop, am I right to have the system as primary and the heat exchanger as secondary? Or should they be switched?</li><li>I could use a taco 007-vr on the polaris side, and loose the bumblebee and secondary loop all-together, but the VR is 3X the cost of the bumblebee. Is the added complexity penny wise and pound foolish? Is there a cheaper circulator that does setpoint variable speed and is brass/stainless?</li><li>I've got both the alpha and bumblebee oriented vertically. That adds a few bends to the system, but it's my understanding it will help ensure air bubbles travel toward the air eliminator. But with both pumps pulling water downhill (and thus pulling air bubbles down too) does it really help anything?</li><li>Are there any other obvious flaws here that are making me look stupid (I've got thick skin, I can take it).</li><li>What should be done about backloss? My understanding is that some of that heat is truly lost, but that much of it is coming right back at you in the form of thermal mass. Is there a rule of thump for how much you get back? I've got slab, crawl space, and second story all in the mix, if that helps any.</li><li>Polaris is available in 34 and 55 gal models. Without the hack, either model will cycle like crazy, taking less than a minute to overcome the 3 degree delta built into the system. With the hack in place, is the extra energy storage of the 55 Gal model worth the extra cost and space?</li></ul>
0
Comments
-
Why
no modulating equipment ? Polaris is a lot of money for no tech . You could lose a pump and a lot of extra labor with some more thought . No worrying about short cycles , better HX inside a packaged unit that just needs programming . Mod Con , better warranty . What's your prevalent need , DHW or space heat ? Somebody already did this work for you .
http://www.htproducts.com/versaflame.html
http://www.htproducts.com/versahydro.htmlYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
Agree
+1 with Rich !0 -
One of these days...
Some day I will disagree with Rich and Gordy. It won't today.
As for the questions,
I think the primary secondary is correct.
I would keep the bumble bee on the system side as a outdoor reset injection mixer. It will keep the system at the perfect output temp.Put an inexpensive stainless circ on the polaris side.
Don't overthink the airbubble thing as long as you are pumping away from the expansion tank, the bubbles wiil be gone before you can believe.
You may need the "thick skin" on the polaris thing.
Not sure about the "backloss" question. some heat is lost to the building, Not an issue. Some up the flue. That is an issue. What is the Afue number?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements