No hot water after pilot out on boiler

AdinP
AdinP Member Posts: 2
Hello,



We noticed last night that there was no hot water for showers. I looked at the boiler and noticed the pilot was out. I it is lit now and several hours later there is still no hot water. I have tried turning the thermostat on the hot water tank up to see if it would kick the boiler on, but no. When I turned the heat on (forced hot water baseboard) the boiler kicked on. Any help is appreciated

Comments

  • Paul48
    Paul48 Member Posts: 4,469
    Information

    Is it a zone valve system, or circulators? In other words, circs for each zone, or one circ and zone valves for each zone?
  • AdinP
    AdinP Member Posts: 2
    No hot water after pilot out on boiler

    one circulator and three zone valves
  • Paul48
    Paul48 Member Posts: 4,469
    W.A.G.

    Maybe an end switch on the zone valve is not being made. Look at the power head on the zone valve. There is probably a manual bypass on the powerhead.
  • Zman
    Zman Member Posts: 7,611
    WAG

    I would second the WAG.

    If it a Honeywell valve the manual lever will not trip it.

    You are going to have to post pictures and a more complete description to get better assistance.

    There are so many different ways to put a system together...
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein