BTU needed on Oil to Gas convesion

Sam1975
Sam1975 Member Posts: 7
I am doing a oil to gas conversion on Peerless boiler. Going to use Wayne conversion burner gun. I have below questions.

- My house was built in 1980 and it is 2500 sq ft. How much BTU I would need. Currently I have 150,000 BTU for oil. I get hot water from this boiler as well.

- Should I get an Outdoor re-set control?

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    edited August 2014
    Oil to gas

    Is this steam or hot water? Do you have enough gas capacity?

    Use the SlantFin app from their website to figure the heat loss of your house, and that will be the BTU size for heating, for hot water only. Steam systems need a different method of calculation.

    For the domestic hot water load, tell us what your usage is ( number of showers, and washer runs) you do each day.--NBC
  • Steamhead
    Steamhead Member Posts: 17,384
    Is that a JO or TW series Peerless?

    If so, or even it it's a later model, that Wayne burner won't work well. Its fan will not develop enough static air pressure to move enough air through the tight flueways in these boilers. You will not get good combustion efficiency and the CO levels may be too high, from incomplete combustion.



    The Carlin EZ-Gas would be my first choice, followed by the Riello gas burner. Beckett just came out with their CG4 but I have not used one, so can't speak to its capability.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    And keep in mind

    that the BTU output from the burner must be within the recommended range for the boiler... you don't give the model number, so we can't help with that.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Sam1975
    Sam1975 Member Posts: 7
    oil to gas

    I have Hot water. Peerless WBV-04-100-WPCL. We six use of shower and 1 use of washer each day.
  • Sam1975
    Sam1975 Member Posts: 7
    BTU needed on Oil to Gas convesion

    I have  Peerless WBV-04-100-WPCL.