engineer
RustyHill
Member Posts: 2
Working on some renovations to an 1920's steam radiator system. At the end of one of the mains, there is a wet main on the drawings and it apparently is under the floor. The return main is next to the steam main. See the attached drawing detail.
Project is to put an elevator where the wet return supposedly is. What options do I have for the wet return except cutting the floor and rerouting? All radiators after the 3 column, 56 sq.ft. will be gone. I think that it is there as a trap for the main. If I get rid of that one also, do I need to keep the wet return?
Return
Here's the answer you hate to here...it depends. Can it be rerouted? Can it be converted into a dry return?0 -
Moving wet return
If the wet return is below the waterline of the boiler, then it can be easily rerouted without regard to slope. Make sure there is a valve and tee on it for flushing purposes.
Is this 1-pipe, or 2-pipe?--NBC0 -
wet return
It's a 2 pipe system with a return from the upper floors at pretty much the same elevation as the steam but this small radiator at the end of the main appears to be there just as a trap. I think I can get rid of it.
Thanks0 -
Check very carefully!
that small radiator at the end of the main to which you refer may be important for getting proper venting of that main. There has to be a way for the air to get out of the steam main -- either into the dry return to which you refer, or into the air.Br. Jamie, osb
- 85.2K THE MAIN WALL
- 55 Biomass
- 72 Chimneys & Flues
- 129 Geothermal
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
