Choices on gas conversion equipment
DBentley
Member Posts: 2
in Gas Heating
We are converting from oil to gas and have received two quotes from trusted plumbers that we have used in the past. Obviously everyone has their preferred equipment, but I was hoping to get some opinions regarding the two systems. I don't want to overspend if they will both perform well, but I don't want to buy the less expensive equipment and have more problems with it.
Background: 1 zone, 2 levels (Basement not heated), 1800 sq ft. Baseboard forced hot water.
Options: Williamson GWC Series 114K net BTUs
Lochinvar WHN-085.
Thank you,
Background: 1 zone, 2 levels (Basement not heated), 1800 sq ft. Baseboard forced hot water.
Options: Williamson GWC Series 114K net BTUs
Lochinvar WHN-085.
Thank you,
0
Comments
-
Equipment
I would prefer the Lochinvar. But more importantly, have the contractor's performed a proper heat loss of your home?0 -
Discussed heat loss but not done
Neither did a heat loss calculation. One said he could if we would like, but he recommended the Williamson based on the current oil furnace we have and the need for at least 100 BTU for the water tank. We have used this gentleman previously and he has done a good job (no need to call again about same issue)
The other did a measurement of our baseboards and said 85 BTU Lochinvar will be plenty (only system he installs due to superiority). This gentleman was recommended by a general contractor (the general contractor was recommended by a friend for another job).
We had a home energy assessment and there is a definite need for updating insulation through the whole house (built in 1961) and a few windows.
Thank you again for your help. It is difficult to know which is the right decision when you have no working knowledge of the field.0 -
Heat loss
A heat loss needs to be done before anything else can be decided. Both contractors have chosen their boiler size with completely wrong methods. You do not measure the baseboards to find the boiler size, and you never trust the size that is currently there. If neither of them can perform a proper heat loss (the most essential factor in a boiler replacement) then what else are they not going to know or do?
Where are you located? We might know somebody in your area.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements