One riser or two?
Pilot RE
Member Posts: 11
I’m replacing the riser(s) and header on my Weil McLain EG-75. The manual recommends a minimum of one 3”
riser and a 3” header. For the next larger boiler in the series, WM recommends
a minimum of two 2” risers and a 3” header. Given that two 2” risers have
slightly smaller volume than one 3” riser, shouldn’t a single 3” riser perform
better? Is there a benefit to using both taps even with a slight reduction in
capacity? The boiler has two 3” taps, and I plan to install a drop header. I am
aware that two 3” risers would be the best, though less affordable, option.
riser and a 3” header. For the next larger boiler in the series, WM recommends
a minimum of two 2” risers and a 3” header. Given that two 2” risers have
slightly smaller volume than one 3” riser, shouldn’t a single 3” riser perform
better? Is there a benefit to using both taps even with a slight reduction in
capacity? The boiler has two 3” taps, and I plan to install a drop header. I am
aware that two 3” risers would be the best, though less affordable, option.
0
Comments
-
two vs one
Two risers pull steam from two different locations making for a more balanced situation. I believe when you pull from one location it usually causes the water level to shift and raise towards that area.
If I was piping it I would without a doubt use two 3" risers into a 4" or 5" header. I piped my EG-45 with two 2's into a 3" header.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
two
I would use two, It will slow down the steam….0 -
If you decide to use 2
they should both be 3 inch. As has been noted, two 2 inch are actually smaller in area than one 3 inch.
There is some advantage to having two, but on the 75 it isn't really necessary, provided that the rest of the header piping and all is correct. I'd put my effort into building a drop header for it, instead of going with two 3 inch -- you'll have better steam quality.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
two 2 1/2" risers would be best with
a 4" header. Two 3" is over kill and squeezing it all into a 3" header would just leave you with high velocity steam.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Piping
According to my charts, I would agree with the 4" header. But, 2.5" risers come up short on capacity for me (180K BTUH @ 20 ft./sec). I would go for two 3" risers. Either way, the manufacturer's suggestion are always much smaller than they should be. I would disregard almost all of their piping sizes.0 -
Thanks
Thanks for the feedback. Any of these options is sure to be an improvement over what is currently installed!0 -
Ouch
Almost anything would be better than that.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Wow
At least you can recoup some of the expense from the scrap copper. Does that thing even work?0 -
Sort of
An appropriate quantity of wet steam is produced.0 -
-
NICE JOB!!!!!! Made me SMILE!!!!0
-
Looks solid, just wondering if you have an equalizer, from that angle I can't see one0
-
...Makes me smile too, especially when it's running and I no longer hear any of the noises I used to.
You can see the equalizer from this angle. (Insulation will be added in a few weeks.)0 -
What a vast improvement over the piping you had before. That's a sweet looking drop header. I think I see an equalizer hiding behind that second riser...yes?
How's the performance? Any noticeable difference in the overall heating of the system?
S.P.Burnham IN6 |one-pipe steam
Boiling water for heat since 2006.0 -
Ha! Looks like you answered my questions as I was asking them. Good Job! Take care. S.P.Burnham IN6 |one-pipe steam
Boiling water for heat since 2006.0 -
Why all the bushings and 45s.. why not cast iron…looks better but,just asking?0
-
SP: I'll have a better idea of performance when it gets colder. My test runs have been brief but positive; it's just too warm to leave the heat on.
JA: Fair questions all. Those take offs aren't as elegant as I'd like, however they were designed to allow condensate to drain back to the header without getting trapped, and the geometry doesn't work with 90s for either main; the ceiling and girder are in the way for the one, the header and main are pitched in opposite directions for the other. There's also very little room to work on that side of the boiler. It was a compromise like every design.0 -
Nice! The dry steam don't care about no stinkin 45's! Have you skimmed it yet? Did you do it yourself?
Rob0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements