Electric Boiler and short cycling
Hilly
Member Posts: 428
Is Short Cycling a big issue with an electric considering it is nearly 100% efficient? I know components will suffer shorter life expectancies but is that the only concern? Am I wrong that short cycling concerns are mainly an efficiency concern?
0
Comments
-
Efficiency and comfort
What kind of controls are on the system? If it's a bang/bang thermostat, you will get greater temperature swings than you would with PWM -- even for a single element. How big is the boiler? For smaller sizes, you can use a line voltage thermostat directly, but adding a contactor for larger elements (up to a point) is not very expensive.0 -
Demand Meter
In addition to SWEI's response,
On premises that are "Demand Metered", is is a good idea to have multiple elements and stage them. Bang Bang thermostats with leave you with very high demand spikes which will raise your rates."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
older style
electric boilers had magnetic contactors, frequent, short cycling wasn't kind to those contactors. Plus the noise and lights dimming
Most of the current electric boilers have triacs controlling them, for variable outputs and soft starts. Triacs, electronic relays, are very rugged devices.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Right, and for older units
you can use a line voltage PWM stat (which has its ownTRIAC) to trigger a zero-crossing solid state relay for larger loads. You can also phase chop (dim) them with 0-10V control signals for full modulation (at the cost of some increase in line noise.) Works well with ODR controls.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements