Condensing cast iron?
RobG
Member Posts: 1,850
How does the Hydrotherm KN series boiler manage to provide high efficiency coupled with cast iron? Granted, it is a manufacturers claim, but up to 99%efficient? Is it a disposable unit, glean the efficiency while it rots out?
I would love a high efficiency cast iron residential unit. How do they do it?
Rob
I would love a high efficiency cast iron residential unit. How do they do it?
Rob
0
Comments
-
RAY
has been around for 6 years or so. No personal experienceBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
rAY
I remember the rAY thread from a few years ago, but has anything come from the CI condensing technology? I can't find anything on the web about the rAY since 2011. It's not on Mestek's website.
How have the KN's been holding up?0 -
Condensing cast iron
There must be two separate heat exchangers, with the cast iron being the primary, and a smaller secondary stainless one to suck the last heat out of the flue gases.
Probably the return water goes to the secondary exchanger first, and then to the primary..
There is probably a low limit on the primary/secondary loop temperature though.--NBC0 -
Peerless
This a RaY in green
http://www.peerlessboilers.com/Products/ResidentialBoilers/Cast922/tabid/211/Default.aspxTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
AFUE
It looks like they are doing it with a secondary heat exchanger.
The KN-2 had an AFUE of 92.7% under the old rules. It looks like 90% under the new rules.
http://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&ved=0CB8QFjAA&url=http%3A%2F%2Flibrary.cee1.org%2Fsites%2Fdefault%2Ffiles%2Flibrary%2F9301%2F2014_March_CEE_Boilers_QPL.xls&ei=WlvdU5esJqP_igLY9YDICg&usg=AFQjCNFUuahDD6wSx18GbqY4-M2AU-7BUQ&sig2=PhfzjcZnHm-qNzb4CODT3Q"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Similar question...
Not trying hijack the thread at all, but I was wondering about a similar question...
We are getting quotes for a new boiler, and one of the recommended units is a Burnham ESC4. It is a cast iron boiler, 85%, and the manual says it can accept return water temps down to 110 degrees. I have always heard that 140 was kind of the standard minimum for cast iron, to prevent condensation from eating the boiler sections.
I know that the unit has electronic controls, and an option for a plug-in outdoor reset sensor. So I was kind of wondering, what am I missing about this? Do they just size the burners so that the flue gas temps stay high enough to prevent condensing at 110 degree return water temps? Or perhaps cycle the circulator so that the water in the boiler can come up to temp faster?
Just curious....if anyone could enlighten a relative noob about this, I'd appreciate it.
Thanks,
Andy0 -
I have some....
experience w/ the Ray. I had some control issues but the factory came through and got that fixed. The specific unit was in a gravity conversion system...loads of CI rads. Huge mass.
No secondary HX.
They are relying on on the thickness of the CI and the pins to hold up. This is a smaller version of the KN series they have had out for years.
The control can do a bunch of different things. The venting is only in stainless. plastic is not allowed.0 -
esc
I believe the ESC and ES2 have similar heat exchangers and have been designed to accept low temp return water.Problem is condensation in the flue.When installing these units I like to put a bypass between supply and return and use a gate valve to increase return temp.0 -
Higher return?
Raising the return gets the boiler out of condensing zone and greatly reduces the efficiency.
Why bother spending extra money for the HE model?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
regarding the ESC
Condensing in the flue...I see. I guess in my situation even that would be minimized since it's a powered direct vent unit and the total flue length will be about 4-6 feet (if that is indeed the boiler I decide to go with).0 -
I may be wrong
I may be wrong but I seem to remember something about siliconized cast iron being used and that helps with the corrosion issues? Once again, I may be wrong but it seems to ring a bell in my noggin. I don't see anything in the product literature though.
Rob0 -
ES2
yes Rob G I rememberr something about siliconized cast iron.I think that was their whole selling point so you could use odr without any problems.I still use odr on the boiler withh great success but am concerned with condensing in flue,ESC i am not familiar with.With bypasss odr will work fine.0 -
CI condensing
I have seen a few installs of the KN and a few in laboratory conditions. There is NO secondary heat exchanger! The burner is along the top of the boiler casings. In the installs that I have seen, they stood up well. Here is the I & O manual:
http://mesteksa.com/fileuploads/Literature/Hydrotherm%20Boilers/KN%20Series%20Boiler/KN-2%20and%20KN-4%20Boiler%20IOM%20(KN-2_4%20IOM2-0714).pdf
In my old home, I had a Viking Junior condense for 5 years with no problems! BTW, It is till condensing nearly 35 years later! Installed in 1929!0 -
condensing cast iron
nbc was right williamson makes the gwc its a cast iron primary heat exchanger and stainless secondary exchanger0 -
not the....
same boiler design. KN series/ Ray has no secondary HX. Williamson and the Weil 90+ is the same boiler....they have a secondary hx.-1
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements