Expanion rate
Techman
Member Posts: 2,144
What is the expansion of the copper lines in a horizontal run 100' long, of 1 5/8" copper discharge line and 1 1/8 liquid line? In inches, please. Ok ,I'll settle for the expansion rate if need be.
0
Comments
-
very nearly
10 microinches per inch per degree F temperature change. Depends a little on the alloy.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Rule of thumb.
Terry, the rule of thumb that we have been using for AC and Refrigeration is 1" per 100' of horizontal run, properly supported. It isn't as exact as Jamie's number, but hasn't bitten me in the rear yet. I will do an expansion loop only if the horizontal run exceeds 150' and it is a heat pump application. In AC only, the temp rise is below the point where it will cause a sufficient expansion to stress the joint.
Good Luck.0 -
Expansion
Thanks Jamie, using your formula, I was closing in on that 1" # that meplumber provided. Yup ,pretty darn close.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements