BTU meter for steam
Andy Stack_3
Member Posts: 39
I have and old church and school off the same steam heating system it is zoned using two 8" zone valves.
The church is renting out the school this year and would some how like to bill the school for there portion of the heating bill. Any ideas
Thanks Andy Stack
The church is renting out the school this year and would some how like to bill the school for there portion of the heating bill. Any ideas
Thanks Andy Stack
0
Comments
-
Condensate meter
Usual arrangement is to use a condensate meter.
I assume each system has a condensate pump pumping to the boiler(s) or boiler feed unit. It should be a simple matter to pump the condensate through a meter and keep track of how much condensate is coming back from the school. Figure 960 BTU/lb of condensate. 1 lb. of condensate = 1 pint of water. 8 lbs = 1 gallon. Hope I got these figures right.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
time the zone valves?
Not accurate but ....0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements