Multiple Circulator & Zone Valve Relays with Post-Purge?
Options
Steamhead
Posts: 18,834
Looked at a HW job yesterday with six circs and four zone valves. The control system for this looks like someone threw a whole bunch of spaghetti onto the wall and it stuck. Since we'll probably be re-wiring this, does anyone know of a mutiple circulator or zone valve relay that will allow the circs to purge some of the heat out into the zones after shutting off the burner?
TIA.
TIA.
Co-Founder, All Steamed Up, Inc.
Baltimore, MD, USA
0
Comments
-
does it have an indirect?
if not the priority relay output on most pump relays has a post purge. I know the Caleffi ZSR has a non-adjustable 2 minute post purge on relay 1Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Make your own
Unless someone has some commercial controls experience, you may be better off getting your own relays/contactors (Grainger's) and making it yourself. I know a real wizard up here in the Philly Suburbs who used to build/service elevators before he started his HVAC career. I've seen him do some interesting things with relays and contactors. Send me a message if you want his info.
Tekmar boiler controls (I know the 374 does) also post purge on the DHW contacts ( think until 10 or 20 degree drop).There was an error rendering this rich post.
0 -
-
Th e Honeywell AQ2000 series does, also the Exp Taco has available plug in cards to do that.0
-
-
-
installing in floor heat for all floors for a new house, used gypsum over pex for the main level and 2nd floor. I will have 5 pumps for the floors, one pump for air handler, one for indirect tank.
counting on not using air handler much,
any ideas for switching relays?
they have a huge shower 5-6 heads, not sure if I want to stop making hot water and switch to floor, 80 gallon tank.1 -
Taco offers several controls to facilitate wiring similar to yours, including the SR506-4 EXP with 120 volt output for up to 6 circulators. It has a post purge feature built into the control, which is unique to the priority zone 6, normally used for DHW. If you prefer, you can use zone 6 for another heat zone, and use the post purge feature for that zone. However, it will not work on all the zones, as you mentioned. Frankly, I don't think anyone makes a control that enables you to purge residual heat, and dump into all the zones. Usually, the purge is synonymous with DHW.
For your reference, I attached the Taco zone control wiring guide which is a great resource when challenged with a wiring issue. Please advise if you have any questions or concerns.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 123 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements