Troubleshoot GVD-6 problem
gazzerp
Member Posts: 14
New steam system installed Aug '12: Utica PEG150; FieldControls GVD-6 Vent Damper; M&M PS802 Low Water Cutoff; M&M MM323 Electronic Water Feeder; Honeywell PA404A Pressure Control; Taco SR501 1-zone Switching Relay; SuperStore SSU-45 Indirect Water Heater.
Boiler failed to ignite at some point yesterday.
Began troubleshooting with vent damper - vent closed, room thermostat and/or SuperStore calling for heat and service switch in (normal) Automatic position:
- Have power (26v) between 4&1 and 4&2 (BLK/BRN and BLK/ORG)
- Motor does not function
Repeated above, this time with switch in (override) Manual position:
- Have power (26v) between 4&1, 4&2 and 4&3 (BLK/YLW)
- Motor functions (vent opens)
- Boiler ignites
I disassembled the unit and saw some minor discoloration around the brown diode/resistor on the circuit board.
Given the above, could the problem be anything other than the damper?
Thanks in advance,
Gary
Boiler failed to ignite at some point yesterday.
Began troubleshooting with vent damper - vent closed, room thermostat and/or SuperStore calling for heat and service switch in (normal) Automatic position:
- Have power (26v) between 4&1 and 4&2 (BLK/BRN and BLK/ORG)
- Motor does not function
Repeated above, this time with switch in (override) Manual position:
- Have power (26v) between 4&1, 4&2 and 4&3 (BLK/YLW)
- Motor functions (vent opens)
- Boiler ignites
I disassembled the unit and saw some minor discoloration around the brown diode/resistor on the circuit board.
Given the above, could the problem be anything other than the damper?
Thanks in advance,
Gary
0
Comments
-
The relay
wired between 4 and 2 is defective. When you go to override (manual) also called hold open the system will work as you are bypassing the relay. When in manual you have a direct feed to the motor which will cause the damper to open and close the two end switches and bring on the equipment.
The diagram in the books is not very good. I have a internal diagram of the damper which I can fax you or e-mail contact me at gastc@cox.net.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements