Vaporstat meltdown

Fizz
Fizz Member Posts: 547
for second time v-stat shorted electrical systerm of gas gun and LWC.  Tech re-installed p-trol.  No significant difference noted, as gauge reading 1-2 oz. Don't know if I should get new stat.

Comments

  • JStar
    JStar Member Posts: 2,752
    Vaporstat

    Did the wires short to ground? Were the control wires replaced the first time this happened?
  • Fizz
    Fizz Member Posts: 547
    Both good

    questions, and I don't know.  Sad to say, ignorance is not bliss.  Had 2 different contractors for each occasion; the first time the tech said if it occurs again it will have to be replaced???  Second occurance different tech didn't know of 1st occcurance, but he said it needs to be replaced.
  • Jamie Hall
    Jamie Hall Member Posts: 24,531
    It would be very wise

    to find the root cause of this problem.  A vapourstat -- or pressuretrol -- is very very simply a microswitch with two wires attached to it.  There is no way that the vapourstat itself can "short" the electrical system of anything else.  It can fail closed (always on) or fail open (never on).



    There's a wiring problem here.  If by shorting the electrical system of a gas gun or LWCO you mean that they somehow got zapped with 120 when they should have been seeing 24, for example, that's not the microswitch -- that's in the wiring.



    The wiring could also short to ground somewhere -- but that really shouldn't damage anything else.  Blow a fuse, maybe...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England