Radiant under 3/4 ply & cement board/tile
MW29
Member Posts: 3
I want to install 1/2" pex to bottom side of 3/4 sub floor plywood . Put cement board on top of plywood & than tile. I intend to use aluminum plate on pex & than insulate under sub floor with 3 or 4 inches of spray foam insulation . Will the heat be able to make it through
3/4 ply wood,1/2" cement board & approximately 1/4" tile to warm home. Doing this on my 1st floor after lifting house( took 1&1/2 feet of ocean through 1st floor from Sandy storm
3/4 ply wood,1/2" cement board & approximately 1/4" tile to warm home. Doing this on my 1st floor after lifting house( took 1&1/2 feet of ocean through 1st floor from Sandy storm
0
Comments
-
Radiant under 3/4 ply & cement board/tile
Spray foam insulation will be sprayed directly on to aluminum covered radiant tubeing0 -
Underfloor plates
will work but there are other products methods that are in the same price range that will be more efficient . Have you had a proper hat loss performed or done one yourself ? This is a must . What type of equipment do you have or wish to use ?You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
MW
Didn't do a heat loss , I have a baxi wall hung unit
It now services cast iron baseboard in part of the house
And radiant heat in one room( lowering temp with mixing valve for radiant)& Argo 4 zone controller-
Was just gonna fill every bay with 2 loops
About 8" apart & aprox 3" away from joists
Keeping each loop aprox 300' at around 6 loops
Area is 18' wide x 33' long part of it has kitchen
Cabs & appliances was gonna shorten up a lil
Under that stuff0 -
Spray foam
I am always concerned about spray foam and pex. The heat from the curing foam can damage the tubing as can the chemical interaction.
I like to seperate the foam with a barrier of foil insulation.
I know SWEI has had success with spray in product directly on the tubes. Perhaps he will weigh in.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Not foam
Wet-spray cellulose (or dry blown, after stapling perforated Tyvek to the bottom of the joists) does work quite well. It's also possible to remove for repairs, unlike foam.
Chemical compatibility is one issue, the other is that small amounts of liquid foam tend to creep between the plates and the subfloor. When those expand, your heat transfer goes bye-bye.0 -
SPF and pex
Plates must be sealed at edges , I use inexpensive adhesive tape for this when SPF is to be used . The first and second layers applied should only be 1 inch lifts , the tubing can handle that easily .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements