Hoffman Loop Incorrect?

FHills
Member Posts: 20
Our Peerless Series 61 steam boiler was installed in September 1998, in a oil-to-gas conversion. While digging through old files, I came across this note from another plumber who examined the boiler in November 1998:
"The Hoffman loop is incorrect. The feed for header should be feed [sic.] from other tapping of Boiler (Top Right 2") because the return is on the left of the boiler."
My father had asked this plumber for a post-installation assessment. My father can't remember if the issue was resolved. The boiler has been in use these last 15+ years. I've posted pictures. Does it look like the Hoffman loop is installed incorrectly?
Note: the picture showing the front of the boiler is an old one. The pigtail has since been changed to brass. Scroll to the end of (<a href="http://www.heatinghelp.com/forum-thread/150421/Questions-regarding-the-main-vent-and-auto-water-feeder-that-cuts-off-the-boiler-every-10-minutes/success">http://www.heatinghelp.com/forum-thread/150421/Questions-regarding-the-main-vent-and-auto-water-feeder-that-cuts-off-the-boiler-every-10-minutes/success</a>)
Thank you very much!
FHills
"The Hoffman loop is incorrect. The feed for header should be feed [sic.] from other tapping of Boiler (Top Right 2") because the return is on the left of the boiler."
My father had asked this plumber for a post-installation assessment. My father can't remember if the issue was resolved. The boiler has been in use these last 15+ years. I've posted pictures. Does it look like the Hoffman loop is installed incorrectly?
Note: the picture showing the front of the boiler is an old one. The pigtail has since been changed to brass. Scroll to the end of (<a href="http://www.heatinghelp.com/forum-thread/150421/Questions-regarding-the-main-vent-and-auto-water-feeder-that-cuts-off-the-boiler-every-10-minutes/success">http://www.heatinghelp.com/forum-thread/150421/Questions-regarding-the-main-vent-and-auto-water-feeder-that-cuts-off-the-boiler-every-10-minutes/success</a>)
Thank you very much!
FHills
0
Comments
-
Hoffman loop?
I honestly don't see a Hoffman [Differential] loop in the pictures... I do see a Hartford loop which is slightly idiosyncratic, but not in itself that bad... although the horizontal bit of header could be a good bit higher without hurting anything.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements