JayHP33
Member Posts: 2
Total heatloss 51000 (BTUH) what range of boiler is acceptable?
CI only.
Thanks
CI only.
Thanks
0
Comments
-
Sizing
You want a boiler that has an I=B=R rating of 51,000 BTU or as close to that as possible.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
DOE output
When you do a heat loss you use the DOE or Gross output not the lowest number net output.0 -
My interpretation
Of which output number to use is if the boiler and piping is in a conditioned space use DOE output, if the boiler, and piping is Not in a conditioned space use I=B=R.
A heatloss should always be done regardless, and has no bearing on which output number you use.
Not disagreeing with Alan just trying to point out the difference between the two output numbers.0 -
Boiler Ratings:
You can use any number you want. Even what some very old times did by holding a pencil at arms length, and a certain distance from the building, and deciding how much of the house the pencil covered. Then, add a section for good measure.
What they tell you in the IBR courses and the IBR H-22 heat loss guide and the #200 piping design manual is that there are three numbers. Gross Input, how much energy you can put INTO the boiler. The DOE is a number that the hated Gub-Ment came up with to make all things equal and stop manufacturers from over rating their boilers. The THIRD measure, IBR is a rating tested and established by the IBR that would always be lower than the other two ratings. Because, when installed, they allowed 1.33% subtracted for piping and pick-up. So unless you had some unusual piping situation, if you had a heat loss of 60,000 BTU's per hour, a boiler with a IBR rating above that, would do the job.
You can use the DOR number but you need to add for piping and pick-up.
You can do the math yourself. There's a resistance value to everything. Add up every fitting, valve, boiler and piping to get a total resistance and subtract some factor from the DOE to get the friction heat loss through the system that the boiler will see.
Or use the IBR number. It will never be wrong.0 -
If you run a mod/con on ODR
Even the DOE rating will have a significant safety margin.0 -
Old news but don't be looking for the IBR Ratings any more
On January 1, 2012, all I=B=R marks were replaced by the AHRI Certified mark. Manufacturers participating in the I=B=R programs must use the AHRI Certified mark, but they have the option of simultaneously using the I=B=R mark until January 1, 2014.
The GAMA Efficiency Rating Certified mark was replaced by the AHRI Certified mark on January 1, 2013, for commercial water heaters, residential water heaters, and direct heating equipment certification programs.
All former ARI Performance Certified marks have been replaced.
No more IBR rating (or AGA), it is now NET AHRI CAPACITY
Input – Efficiency Loss = Heating Capacity (DOE Output) – 15% Piping Loss = Net AHRI Capacity0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements