HOME OWNER

DRAMDRAM Member Posts: 1
Can anyone help me with a heating problem? I have a Consolidated Ind. gas furnce model HBA080ND4R. in heating mode the blower will not come on auto? I have checkdthe klixon and the high limit and they are ok? the blower wiol work in the cooling mode? please help thanks

Comments

  • Tim McElwainTim McElwain Member Posts: 4,436
    Is the burner coming

    on when the thermostat calls for heat? Does the hot surface igniter glow? Your furnace has an Electronic Fan Timer which delays bringing the blower on for either 30 or 60 seconds. For that to happen the combustion air blower must come on the pressure switch has to close and then the igniter glows and hopefully ignites the main burner. The next thing to happen is for the system fan to come on either 30 or 60 seconds later. Check this sequence and see what is not happening.