Can anyone help me with a heating problem? I have a Consolidated Ind. gas furnce model HBA080ND4R. in heating mode the blower will not come on auto? I have checkdthe klixon and the high limit and they are ok? the blower wiol work in the cooling mode? please help thanks
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 564 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
on when the thermostat calls for heat? Does the hot surface igniter glow? Your furnace has an Electronic Fan Timer which delays bringing the blower on for either 30 or 60 seconds. For that to happen the combustion air blower must come on the pressure switch has to close and then the igniter glows and hopefully ignites the main burner. The next thing to happen is for the system fan to come on either 30 or 60 seconds later. Check this sequence and see what is not happening.