Thermo couples

in Gas Heating
I have a utica gas hot water boiler, model #M75AGB, serial # BB04404. What could cause the thermo couple to not work? I had to replace it three times since december. Any help would be great. Tom
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 564 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
is this a standing pilot boiler or spark ignition?
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
It is a standing pilot boiler>
or thermocouple too deep into the flame because something got bent can cause issues. are you sure it is the thermocouple that is the problem?
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
Yes because i try to clean it will not light, i change it all is fine for a few months , then it will not light.
I seriously doubt that you encountered that many bad t'couples.You need a Millivolt meter to test how much electricity( volts ) is being produced by the pilot flame.
Thanks everyone for the help. Tom
a thermo pile, right?
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
It is a thermo couples.
a multi-meter that will measure millivolts? If so then go up and click resources, then library and look for Tims closet there is a procedure for checking thermocouples there.
Tim thank you for the info. Tom
Utica boiler has a tendency to burn up thermocouples especially when it is cold and the boiler is running a lot. There is a thermocouple from Johnson (now Baso Gas Controls LLC) it is the K16LRA nickel plated corrosion resistant and hi-temp thermocouple. It is a little more expensive but it will out last most T'couples 3 to 1.
Tim , thank you.
If the chimney is not venting properly, it can spill CO2, which displaces O2 causing pilots to snuff out.