Bryant Plus 90 Code 33 to 13 but doesn't seem to be the limit switch.
swing4thefence
Member Posts: 1
in Gas Heating
So I have this Bryant Plus 90 that is blowing cold air continuously.
Last night I opened it up. I found 1 flame rollout sensor on the side of the burner box and then the limit switch that goes in to the heat exchanger. I tried pushing the button on the FRS with no success. Next I pulled the two red wires off and jumped them, no success. I used a meter and verified continuity and replaced the wires.
NExt I pulled the wires off the auto-resetting limit switch and jumped them with no result. I tested it for continuity and my meter read 508. Weird to me because usually it shows 1 for open circuit and 0 for closed.
So I set my meter on 200Vdc and tested for voltage across the red wires. I got 0 volts in each place. Then I went to the Control board and found where the red wires come out. I found terminals that I could put my probes on and still got 0 volts.
This leads me to the question of what am I missing? 0 volts tells me that there is an open in the circuit but the circuit is closed at the two interruption points I identified. is there a third interruption point I missed?
Last night I opened it up. I found 1 flame rollout sensor on the side of the burner box and then the limit switch that goes in to the heat exchanger. I tried pushing the button on the FRS with no success. Next I pulled the two red wires off and jumped them, no success. I used a meter and verified continuity and replaced the wires.
NExt I pulled the wires off the auto-resetting limit switch and jumped them with no result. I tested it for continuity and my meter read 508. Weird to me because usually it shows 1 for open circuit and 0 for closed.
So I set my meter on 200Vdc and tested for voltage across the red wires. I got 0 volts in each place. Then I went to the Control board and found where the red wires come out. I found terminals that I could put my probes on and still got 0 volts.
This leads me to the question of what am I missing? 0 volts tells me that there is an open in the circuit but the circuit is closed at the two interruption points I identified. is there a third interruption point I missed?
0
Comments
-
The system you have
is 24 volts so I would set the meter on AC volts to start with.0 -
more limits
I think if you follow the wiring diagram, you will find another limit inside the burner enclosure box. When I worked on those, most of the limit wires were red and just made a big loop thru them all then back to control board. Depending on the age you may want to get a carrier / Bryant tech to check this out.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements