I have to build a false water line on a upcoming boiler replacement.... But I will not be able to bring the inverted loop up 4 feet per dan's book the lost art. ...I will only be able to go up 30 inches to the top of the inverted loop seal then I have the 28 inches for the "A" dimension. Will it work as it should? Do I have another option if it can't work? Thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    will it

    put the wet returns under water at the height you want to use? if so you should be fine..
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • JStar
    JStar Member Posts: 2,752
    FWL

    I usually only cover the returns with a few inches of water with a false water line. This practice is mainly influenced by the super low basements we always seem to be working in. With the FWL being equalized on both sides, you shouldn't have a problem as long as the returns are covered with water, and the FWL connection is an appropriate A Dimension below the steam mains.
    Paul S_3
  • Paul S_3
    Paul S_3 Member Posts: 1,274
    Thanks

    Thank you guys for help. .... I will post pics when job complete Paul S