Idea's as to getting steam horizontally to farthest radiators at other end of house on first floor?

Options
Athana
Athana Member Posts: 105
At the other end of house on first floor are two radiators in same room that will not heat up readly.The room above this space also is slow to heat.

They are over an enclosed crawl space.

The valves were replaced and Gorton vents with biggest holes installed

The radiators on the third floor have no trouble heating though.They get instant heat though far away as well.

These radiators only heat up when boiler is cranking full out. Usually they are cold.



The plan is to drill/tap and add an additional vent to those two radiators as per suggested in Dan Holohans book..and possibly insulated pipes under crawl space..

But what else can it be??

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,552
    Options
    Pipes not insulated

    in the crawl space?  !!!  That's the place to start, right there.  They are condensing like mad and it will naturally take a while for the steam to get there!



    An object lesson in why steam mains need insulation...



    The extra vents will probably help, too.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 16,948
    Options
    Are there

    any main vents on the steam main feeding this area?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Mark N
    Mark N Member Posts: 1,115
    Options
    Cold Room

    You state in another thread that JStar put in a gas boiler for you. You should have him look it over and get it fixed.
  • JStar
    JStar Member Posts: 2,752
    Options
    Steam

    Sometimes, a second opinion is needed to confirm my own suggestions.
  • Mark N
    Mark N Member Posts: 1,115
    Options
    Cold Room

    All your going to get here are opinions from people who haven't actually seen what is going on. We know the pipes are uninsulated and in a crawl space. Are the pipes large enough to handle the connected radiation? Are the pipes properly pitched? Does every rad have its own runout from the main or do they share the same runout? Not enough info given to really give a good suggestion. If your expert opinion is to tap and add a second vent and insulate the pipes, then that is what should be done. If that is only a part of your recommendation then we don't have the whole story.
  • Jamie Hall
    Jamie Hall Member Posts: 23,552
    Options
    If Joe

    is on this one, he's the chap I'd listen to!  He's one of the best in the business, and if he's seen it... 
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Athana
    Athana Member Posts: 105
    Options
    Its a Mystery

    Joe is working on it..its trial & trial.. but I figured to ask here and maybe there is something that he has not thought of. As it is like a detective thing.

    The crawl space undernieth has an open hatch to regular basement which we keep open so it is not really stone cold in there.

    The owner previous to the people we bought the house from, say that that room had always heated up..!

    But the last owners did not clean the boiler and one day it had a soot explosion..

    It got everywhere in the house...maybe this soot has somehow clogged the piping going in that direction??

    But I think that area always had trouble, as on that line is extra vents taped into that pipe.

    This is a challenging thing
  • ChrisJ
    ChrisJ Member Posts: 15,866
    Options
    Just a guess

    Only thing I can think of is vent all of the other radiators slower, or at least slow a few down.



    That and insulate those pipes! If you're killing steam faster than you're making it some radiators will never get hot. This is why slower venting may help.



    My guess is once most of the other radiators are hot there is finally some extra steam left over to go to the cold ones.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment