Athana
Member Posts: 105
At the other end of house on first floor are two radiators in same room that will not heat up readly.The room above this space also is slow to heat.
They are over an enclosed crawl space.
The valves were replaced and Gorton vents with biggest holes installed
The radiators on the third floor have no trouble heating though.They get instant heat though far away as well.
These radiators only heat up when boiler is cranking full out. Usually they are cold.
The plan is to drill/tap and add an additional vent to those two radiators as per suggested in Dan Holohans book..and possibly insulated pipes under crawl space..
But what else can it be??
They are over an enclosed crawl space.
The valves were replaced and Gorton vents with biggest holes installed
The radiators on the third floor have no trouble heating though.They get instant heat though far away as well.
These radiators only heat up when boiler is cranking full out. Usually they are cold.
The plan is to drill/tap and add an additional vent to those two radiators as per suggested in Dan Holohans book..and possibly insulated pipes under crawl space..
But what else can it be??
0
Comments
-
Pipes not insulated
in the crawl space? !!! That's the place to start, right there. They are condensing like mad and it will naturally take a while for the steam to get there!
An object lesson in why steam mains need insulation...
The extra vents will probably help, too.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Are there
any main vents on the steam main feeding this area?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Cold Room
You state in another thread that JStar put in a gas boiler for you. You should have him look it over and get it fixed.0 -
Steam
Sometimes, a second opinion is needed to confirm my own suggestions.0 -
Cold Room
All your going to get here are opinions from people who haven't actually seen what is going on. We know the pipes are uninsulated and in a crawl space. Are the pipes large enough to handle the connected radiation? Are the pipes properly pitched? Does every rad have its own runout from the main or do they share the same runout? Not enough info given to really give a good suggestion. If your expert opinion is to tap and add a second vent and insulate the pipes, then that is what should be done. If that is only a part of your recommendation then we don't have the whole story.0 -
If Joe
is on this one, he's the chap I'd listen to! He's one of the best in the business, and if he's seen it...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Its a Mystery
Joe is working on it..its trial & trial.. but I figured to ask here and maybe there is something that he has not thought of. As it is like a detective thing.
The crawl space undernieth has an open hatch to regular basement which we keep open so it is not really stone cold in there.
The owner previous to the people we bought the house from, say that that room had always heated up..!
But the last owners did not clean the boiler and one day it had a soot explosion..
It got everywhere in the house...maybe this soot has somehow clogged the piping going in that direction??
But I think that area always had trouble, as on that line is extra vents taped into that pipe.
This is a challenging thing0 -
Just a guess
Only thing I can think of is vent all of the other radiators slower, or at least slow a few down.
That and insulate those pipes! If you're killing steam faster than you're making it some radiators will never get hot. This is why slower venting may help.
My guess is once most of the other radiators are hot there is finally some extra steam left over to go to the cold ones.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements