Oversized - can you check my math
Si_zim
Member Posts: 40
I have a ThermoFlo GSA-150 - which has 125k net BTUh capacity apparently.
I attach a file with radiator CF/BTU workings. Pipes are pretty well insulated so I think the default pickup will be fine. Seems to total 242sq ft and 58k BTU.
There is also a zone of hot water baseboard 29ft long for roughly 15k BTU.
So my estimate is that I have about 73k BTU of radiation... boiler is way oversized.
The addition with the baseboard got chilly during the recent cold spell so I think they did not spec it right for the windows, cathedral ceiling etc. So I would like to swap out the basic slant fin for the Multi/Pak jumbo fins for about 800BTU/lineal ft (total of 24900) and move some of the old slant fin down to the basement for another 9k BTUs there.
This comes to a total of 92k BTU - which should still be safely under the boiler's net capacity... hopefully warmer all round and less cycling on the steam side.
If anyone could review in case I missed something - would appreciate it
I attach a file with radiator CF/BTU workings. Pipes are pretty well insulated so I think the default pickup will be fine. Seems to total 242sq ft and 58k BTU.
There is also a zone of hot water baseboard 29ft long for roughly 15k BTU.
So my estimate is that I have about 73k BTU of radiation... boiler is way oversized.
The addition with the baseboard got chilly during the recent cold spell so I think they did not spec it right for the windows, cathedral ceiling etc. So I would like to swap out the basic slant fin for the Multi/Pak jumbo fins for about 800BTU/lineal ft (total of 24900) and move some of the old slant fin down to the basement for another 9k BTUs there.
This comes to a total of 92k BTU - which should still be safely under the boiler's net capacity... hopefully warmer all round and less cycling on the steam side.
If anyone could review in case I missed something - would appreciate it
0
Comments
-
tried to upload
Well I tried to upload as XLSX and RTF files with no luck... will try to post the table somehow0 -
Hope this works
RADIATOR Height in Style no width section sqf/sec rad sqf EDR RAD CF BTUh
Grnd floor bath 19 tube 4 4.5 14 1.7 23.8 0.3094 5712
Sitting rm left 22 col 3 9 14 3 42 1.05 10080
Sitting rm right 22 col 3 9 14 3 42 1.05 10080
1st floor bath 25.5 tube 5 8 6 2.7 16.2 0.2106 3888
Front bed 19 tube 4 4.5 20 1.7 34 0.442 8160
Master bed 21 tube 4 4.5 22 1.7 37.4 0.4862 8976
Back bed 25.5 tube 5 8 8 2.7 21.6 0.2808 5184
Attic 37 col 3 9 5 5 25 0.625 6000
Total Sq f 242 Total BTUh 580800 -
It's so much simpler
to work with EDR, which boilers are rated in, rather go through the headache of adding a pickup factor (or maybe not... or maybe a bigger one... or...)
What is the EDR rating of that boiler? Compare that with the EDR for your radiation, and there you are. If the boiler is over, then you can go and convert the excess EDR to BTU and use that number to see what you can do with the addition...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
boiler capacity
You can safely add that baseboard.0 -
Boiler manual says 394ft EDR
Not sure what normal slant fin baseboard EDR is but seems like I do have more than enough capacity.
Wonder why they had such a beast installed0 -
Down fire?
Even with my plan to increase baseboard it seems the boiler may still be a bit oversized. I guess over time efficiency may drop and it is good to have a safety margin - but wondering if it would be more efficient to down fire it a bit also?
Does anyone have experience with Thermoflo (standing pilot) or is an agent for them - so I can find out if that is a possibility?
Thanks again0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements