What is it ,really?
Techman
Member Posts: 2,144
On a Honeywell Aquastat # L8148E1265 which has the Molex wire harness to/from the HW flue damper. I had a no heat call. By pushing sideways on the male Molex(harness) to female Molex of the HW aquastat I was able to establish contact which lasted till the next day when I replaced the HW control. There was instant ignition when plugging in the original/old Molex plug into the new Aquastat control.So, what is the actual fault ? Is there"corrision/oxydiation " between the m x f of the Molex that could be cleaned with a small enough copper tubing cleaning brush OR is there an actual fault in the aquastat/molex?
0
Comments
-
Molex Plugs....
You have run into a plug that may or may not have a clean connection. I am not a fan of molex plugs since I can not be sure that the solid connection is there. Corrosion, broken plastic clips etc... are a pain in the but. Basically just like a solid state CB, if you check your connection and the circuit you are looking for is not where you need it, or doesn't seem complete the circuit, ya have to replace it.
Peace;
Mike T.0 -
These 8148E controls
with the damper plug are all having the same problem with poor connections as time goes on. One thing is they have to be handled very gently as pulling on them to get the plug out can sometimes loosen connections. I have actually on several occasions removed the Molex and rewired the damper with out the plug. It is not a problem as the internal resistor in the 8148E is already blown so no safety is involved.0 -
Common issue
Over the last 20+years i have found the most common cause of failure in honeywell aquastats to be poor solder connections at the rear of the board. Wherever a pin comes through the board, the solder connection tends to crack or pull loose. I carry a soldering iron and some supplies on my truck in case i dont have a replacement control so i can get the heat back on.0 -
poor solder connections on the board
I had a similar no heat call.either when the place was robbed of all it's copper or when the owner tried to get it to run by pulling on connections. I narrowed it down to the solder connections.remove all wires,unscrew board from body,bend tabs and carefully pull it from it's case without breaking the aquastat capillary tube.find connects at back of board and resolder.There was an error rendering this rich post.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements