Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Plumber

Lu
Lu Member Posts: 1
Hi I have problem with a hot water heating system it has honeywell zone valves and one of them are banging or a hammer effect when it closes .

Any solutions .

Comments

  • Zman
    Zman Member Posts: 7,611
    Backwards

    First thing to check is the arrow on the side and the arrow on the circulator. They should be going in the same direction.

    A picture would help.

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein