Plumber

Lu
Lu Member Posts: 1
Hi I have problem with a hot water heating system it has honeywell zone valves and one of them are banging or a hammer effect when it closes .

Any solutions .

Comments

  • Zman
    Zman Member Posts: 7,610
    Backwards

    First thing to check is the arrow on the side and the arrow on the circulator. They should be going in the same direction.

    A picture would help.

    Carl