radiant heat in attached garage
mallen
Member Posts: 7
Built a new home 2 years ago.
General Contractor installed 1/2" Oponor AquaPex, part number 1060500 (non oxygen barrier) pex in concrete
1,300 square feet
3 loops of 300' (actually I don't know for sure what length the loops are, I found an empty box so all I know is the tubing came in 300' rolls)
The 3 loops return to the basement
SlantFin heat loss calculation: 37,442 btu/hr (thanks for the advice)
I have an A.O.Smith natural gas hot water heater (HWH) that has outlets on the side for radiant heat, etc., and is used for the hot water in the house. I would like to create a loop with a heat exchanger and a separate stainless steel circulator to transfer heat to the radiant system. Will the HWH water be hot enough? I would like to keep the garage around 60 degrees using a slab sensor.
Then on the other side of the heat exchanger, using a pressure relief valve, air separator and a potable expansion tank (close to the circulator) and allowing plenty of "straight" piping (figuring at least 5") on each side of the circ, can I use 3/4" pex to go from the circ to the manifold? And maybe from the heat exchanger to the drain/fill valve?
Sizing the circulators is so confusing! I tried using the formulas I found, but came up with some goofy numbers! I found someones system that sounded close and used their information. Their head loss was 9 in the tubing and added 2 for the 90's, tubing, etc. That seems high to me, but what do I know?
Thank you, in advance, for your advice and help! I've been a lurker for a while on this site, and there's a lot of good information.
General Contractor installed 1/2" Oponor AquaPex, part number 1060500 (non oxygen barrier) pex in concrete
1,300 square feet
3 loops of 300' (actually I don't know for sure what length the loops are, I found an empty box so all I know is the tubing came in 300' rolls)
The 3 loops return to the basement
SlantFin heat loss calculation: 37,442 btu/hr (thanks for the advice)
I have an A.O.Smith natural gas hot water heater (HWH) that has outlets on the side for radiant heat, etc., and is used for the hot water in the house. I would like to create a loop with a heat exchanger and a separate stainless steel circulator to transfer heat to the radiant system. Will the HWH water be hot enough? I would like to keep the garage around 60 degrees using a slab sensor.
Then on the other side of the heat exchanger, using a pressure relief valve, air separator and a potable expansion tank (close to the circulator) and allowing plenty of "straight" piping (figuring at least 5") on each side of the circ, can I use 3/4" pex to go from the circ to the manifold? And maybe from the heat exchanger to the drain/fill valve?
Sizing the circulators is so confusing! I tried using the formulas I found, but came up with some goofy numbers! I found someones system that sounded close and used their information. Their head loss was 9 in the tubing and added 2 for the 90's, tubing, etc. That seems high to me, but what do I know?
Thank you, in advance, for your advice and help! I've been a lurker for a while on this site, and there's a lot of good information.
0
Comments
-
probably not
I presume the heat exchanger will have circulators on both sides? All just to heat a garage?0 -
correct
a circulator on both sides of the heat exchanger0 -
and yes
all just to heat the attached garage0 -
The good folks
at Taco have exactly what you need for your application. http://www.taco-hvac.com/uploads/FileLibrary/X-Pump-Block.pdf
Harvey0 -
Wow,
you're right, perfect, expensive, but perfect!0 -
If I'm reading the instructions right
the system requires an air separator, expansion tank and pressure relief valve on both the supply and return lines on the X-Pump Block side of the system?0 -
Let's call
the water heater side "primary" and the radiant side "secondary".
You need the expansion tank, PRV (fill valve), air separator on the secondary side return line.
For the primary side.
If you have city water your water heater should already have an expansion tank. If it doesn't put one on. If you have well water, you will already have an expansion tank in place.
Also install these on the primary supply and return. http://www.webstonevalves.com/default.aspx?page=customer&file=customer/wecoin/customerpages/balldrain.htm
That will allow you to clean the mineral deposits from the primary side of the heat exchanger.
Another thing. What make and model is this water heater? Some work for these applications and some don't.
Harvey0 -
A O Smith nat gas water heater
Brand is A O Smith
Model is GPHE 50 series 1000 -
You should not
have a problem with that model.
Run a good outdoor reset curve on the Radiant to minimize short-cycling the water heater.
Harvey0 -
FWIW...
it may be much simpler and give you less headaches to just install a separate water heater just to do the radiant. no need for HX and extra circ pumps. May be less money and your hot water supply will not be compromised.0 -
kiss
I strongly agree with kcopp. Simpler,cheaper. You'll probably operate the heater at coolest setting. With recirculated water the heater will probably last longer than the house. Plus you save pressure drop through exchanger.0 -
I hear what you're saying,
but I was hoping to avoid that situation. I do have natural gas in the basement, but all my appliances are high efficiency and vented through PVC.
How much compromise would I experience using the HX? I ignorantly assumed that once the slab would get up to temperature, it wouldn't be much of a compromise.
I looked online at electric boilers that would produce 40K btu/hr, but they're almost as much as the HX.
This upgrade may get tabled for a while. I just wanted a little more comfort in my garage.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements