Forgot to put water in the pigtail
Clank Clank
Member Posts: 30
Well, more accurately, i didn't know i was supposed to put water in there before reconnecting it. Seems as if the gauge (not the low pressure one yet) is working as before as is the pressuretrol (which is to say not working accurately, .....just as before).
Do i need to take it apart again and put some water in there or would that happen naturally over time?
Do i need to take it apart again and put some water in there or would that happen naturally over time?
0
Comments
-
oops...
Well, you are not the first one to do that!
Probably no real harm, as the components are probably rated for steam. If you feel like fiddling, though, it would be better...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Gauges may not like steam
I'm sure there are gauges rated for steam, but the low-pressure gauges I've looked at all say maximum temperature of 140-160 F. So might be good to have water in there.
But I wonder if it could fill up just by condensation, on its own?0 -
It will
fill on its own, but it will take awhile. If you are at all concerned -- and perhaps rightly so! -- the best solution is to take it off again, put water in it, and put it back. Won't take that long.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
In my experience.....
the fluid that the gauge sees doesn't matter. I've had this discussion in the past with customers concerned about weather the gauge was seeing air pressure or water pressure.
To confirm my opinion, I just had a phone conversation with a tech rep at Ashcroft Gauge. His info was as I suspected, the fluid doesn't matter. Standard Bouirdon tube gauges are good for temperatures up to 250 degrees F., although there is a slight accuracy loss at the high end of this temperature range.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
Ashcroft vs. Wika
The Wika gauges that a lot of us got from gaugestore.com are capsule gauges. They're a little more prone to metal fatigue and temperature distortion. I wish I'd looked at the Ashcroft gauges first. They're more expensive, but you get what you pay for.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Pigtail at water level
With my pigtail at water level I can feel the temperature difference going around the loop.
The loop section toward the boiler is warm and the loop section after the water is cool to the touch.
If you haven't taken it apart you can feel the pigtail loop and see if you feel a temperature difference from one end to another.
If it's warm or hot all the way around, then there is no water or condensation built up.
my2cents.0 -
Steam
We also need to remember unless the gauge is screwed directly into the boiler it is doubtful steam ever makes it to the gauge or pressuretrol even with an empty pigtail. The piping is full of air which isn't leaving any time soon. Sure, over a few cycles it will probably work its way out but I doubt before the pigtail fills with water.
I filled mine first, but I really doubt it matters.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Not a problem
When I installed my 0-3 Wika on the old Burnham v75 I forgot to fill the pigtail before mounting the gauge. I remembered it a few days later and checked the pigtail and it never gets all that hot. The area screwed into the boiler is very hot but the part near the T that feeds the gauge and vaporstat is just warm
The gauge and vaporstat have been moved to my Sith boiler and are both doing fine after four years of faithful service.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
pigtail
If I had to ballpark it, I'd say I myself have installed about 100 residential, well-functioning, steam boilers in the last 20 years. My company's installers, who've learned from me and barely deviate from my methods in the least bit, have about another 500 under their collective belt.
I've never once put water in a pigtail.
Don't invent things to worry about. Water will get there on its own and it's not going to make a bit of difference.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements