Well, more accurately, i didn't know i was supposed to put water in there before reconnecting it. Seems as if the gauge (not the low pressure one yet) is working as before as is the pressuretrol (which is to say not working accurately, .....just as before).



Do i need to take it apart again and put some water in there or would that happen naturally over time?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,373
    Options
    oops...

    Well, you are not the first one to do that!



    Probably no real harm, as the components are probably rated for steam.  If you feel like fiddling, though, it would be better...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • [Deleted User]
    Options
    Gauges may not like steam

    I'm sure there are gauges rated for steam, but the low-pressure gauges I've looked at all say maximum temperature of 140-160 F.  So might be good to have water in there.

    But I wonder if it could fill up just by condensation, on its own?
  • Jamie Hall
    Jamie Hall Member Posts: 23,373
    Options
    It will

    fill on its own, but it will take awhile.  If you are at all concerned -- and perhaps rightly so! -- the best solution is to take it off again, put water in it, and put it back.  Won't take that long.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Pumpguy
    Pumpguy Member Posts: 661
    Options
    In my experience.....

    the fluid that the gauge sees doesn't matter.  I've had this discussion in the past with customers concerned about weather the gauge was seeing air pressure or water pressure. 



    To confirm my opinion, I just had a phone conversation with a tech rep at Ashcroft Gauge.  His info was as I suspected, the fluid doesn't matter.  Standard Bouirdon tube gauges are good for temperatures up to 250 degrees F., although there is a slight accuracy loss at the high end of this temperature range. 
    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    Options
    Ashcroft vs. Wika

    The Wika gauges that a lot of us got from gaugestore.com are capsule gauges. They're a little more prone to metal fatigue and temperature distortion. I wish I'd looked at the Ashcroft gauges first. They're more expensive, but you get what you pay for.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • rrg
    rrg Member Posts: 37
    edited January 2014
    Options
    Pigtail at water level

    With my pigtail at water level I can feel the temperature difference going around the loop.



    The loop section toward the boiler is warm and the loop section after the water is cool to the touch.



    If you haven't taken it apart you can feel the pigtail loop and see if you feel a temperature difference from one end to another.



    If it's warm or hot all the way around, then there is no water or condensation built up.



    my2cents.
  • ChrisJ
    ChrisJ Member Posts: 15,734
    Options
    Steam

    We also need to remember unless the gauge is screwed directly into the boiler it is doubtful steam ever makes it to the gauge or pressuretrol even with an empty pigtail.   The piping is full of air which isn't leaving any time soon.  Sure, over a few cycles it will probably work its way out but I doubt before the pigtail fills with water.



    I filled mine first, but I really doubt it matters.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • BobC
    BobC Member Posts: 5,479
    Options
    Not a problem

    When I installed my 0-3 Wika on the old Burnham v75 I forgot to fill the pigtail before mounting the gauge. I remembered it a few days later and checked the pigtail and it never gets all that hot. The area screwed into the boiler is very hot but the part near the T that feeds the gauge and vaporstat is just warm



    The gauge and vaporstat have been moved to my Sith boiler and are both doing fine after four years of faithful service.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • JohnNY
    JohnNY Member Posts: 3,231
    Options
    pigtail

    If I had to ballpark it, I'd say I myself have installed about 100 residential, well-functioning, steam boilers in the last 20 years. My company's installers, who've learned from me and barely deviate from my methods in the least bit, have about another 500 under their collective belt.



    I've never once put water in a pigtail.



    Don't invent things to worry about. Water will get there on its own and it's not going to make a bit of difference.