alliance running cold
bluemoon
Member Posts: 40
I have 2 Burnham Alliance 55 piped to Apline condensing boilers. Both run cold after running a shower for 10 minutes. I understand that it maybe that I'm drawing 5gpm that the system can't keep up (as advertised) but here is my question....the water from the tank has run cold even though the supply & return pipes are too hot to hold. Why is there no heat transfer? Shouldn't the water be at least lukewarm?Seems that the tank only heats when there is no demand?
0
Comments
-
Questions
Both the alpine and the burnham have high head losses. Is the circulator sized correctly? Is it piped with DHW priority?
What is the output of the boiler during a dhw call? What is the delta t?
Could the coil be calcified?
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I have run....
into a "limed" coils on the Top Performers before....(same as the alliance) This was on city water. It may have not been calcium but it sure did effect heat transfer. Nice thing is that the coil is removable and you can clean it up.0 -
alliance
Both brand new
Tried all 3 speeds on grundfos
Piped directly off header with priority
Supply & return both red hot0 -
alliance
you need a minimum of 1" piping and if using grundfoss use the 26-99.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements