Bryant 987
Phil Yarbrough_2
Member Posts: 20
in Gas Heating
Anyone have any input on a new Bryant 987, fault code #41 . Never locked out just notified twice in a month.
Blower motor fault. Not getting up to speed.
Is the filter clean? Is the blower making any restrictive noises? Did the installers check the static pressure of the system on start-up? Might be a poor duct system.0 -
987
987ma66100v21a-b
retrofit. no blower noise. static .1 low, ,15 high. changed blower module after 1st fault.
Two return drops.0 -
Static
Where was the static pressure test taken?0 -
Are you
Reading the fault at the furnace or Tstat?0 -
Static
Static via stat. Fault shows at both via recall. Component test shows everything good.0 -
There are
Fifty steps in Bryants service book for trouble shooting error code 41. Blower failed to reach 250 rpm or failed to communicate in 30 seconds. My guess is you have a "Failure to communicate" as they say in the movie. The service gude says to replace the Modual and motor togeather in all instances not one or the other. looking over the guide the service tech would need at least 3 hours to perform a proper check of that motor and need special equipment.0