burning out transformers
ruralman
Member Posts: 5
We have replaced the transformer 4X on a Weil-McClein spark ign hot water boiler but it only works for a day or so. Checked wiring according to manual, checked for any irregular/stray voltage on 110v power supply, therm wiring and grounds, also replaced the power module, still can't stop trans from cooking. Anyone run across a problem like this?
0
Comments
-
amp meter
I would put an amp meter on the load side. Something must be overloading the transformers. You have to find out what that is.0 -
xformers
Ohm out both sides of the bad xformers. How about installing a lo volt/lo amp fuse or circuit breaker in the lo volt side ? In the power leg of the 24v xformer.0 -
Homeowner
I'm a homeowner and not a pro so keep that in mind.
However the first thought I had was does the thermostat have a common going to it and have you inspected the thermostat wiring and the thermostat? If it has a common I see no reason the thermostat and or its wiring couldn't randomly cook transformers.
Just an idea I figured it couldn't hurt to offer.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Fuse
For starters, put a fuse on the LV side. Fuses are cheaper than transformers.
Did something else change in the system?
A new t-stat?
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Is the...
transformer being used specifically flor the controls within the boiler? Not any external zone valves or relays? The fuse idea is really a must and you need to find out what the amp load is on the secondary. Any water drips within the boiler cabinet? Solid wire connections on the primary and secondary circuits?Steve Minnich0 -
burnt transformers
Thanks for the advice and suggestions. There have been no changes to the system according to the home owner, no zone valves (single zone), and no voltage coming back from the t-stat. Should I install fuses on both wires coming out of the lo-volt side of trans? What would the ohms tell me?0 -
Ohms law...
See this
http://commons.wikimedia.org/wiki/File:Ohm's_Law_Pie_chart.svg
If you know 2 things, you can find the third.
Transformers are rated in VA, which roughly equals Watts.
If you know the voltage, and the resistance in ohms, you can determine the amperage potential. If it exceeds the VA capacity of the transformer, then you must either reduce load (check gas valve coil) or increase VA of the transformer.
The Ohms Law pie chart gives you this ability. Grab a calculator, you will need it.
METhere was an error rendering this rich post.
0 -
Check the doorbell
In my 30 years, I've occasionally seen doorbells wired to the transformer and thus be a really hard thing to diagnose when they have a short.0 -
burnt transformers
I've already checked for any other transformers, traced the t-stat wires from boiler to t-stat, even ran a temp. dedicated feed to boiler to no avail. The homeowner was finally able to get in touch with the original installer and he recommends changing the gas valve.0 -
LWCO
Does this boiler have a Guard Dog low water cut off? ( round black cylinder - red and green LED's )
If it does replace it NOW - they are known to burn out transformers.
I would think the last part to cause the problem to be the gas valve.
Wires shorted to ground, bad LWCO or vent damper.0 -
burnt transformer
already eliminated the LWCO from the wiring. The power module does not indicate any problems on the LED panel, it just goes completely blank once the trans. goes.0 -
Easier to measure amperage
Typically, for a 40 VA transformer, the amperage of the control (low voltage) circuit should not exceed. 1.67 Amps (40VA/24V). For a 20 VA transformer, the amperage should be no higher than 0.83 Amps (20VA/24V).
This is assuming a 24-volt reading at the transformer's secondary.
As others have mentioned, a fuse on the low voltage side of the transformer is ALWAYS recommended. They are much cheaper than transformers.
And only one fuse is needed on the low voltage side. No need for two.There was an error rendering this rich post.
0 -
They make
transformers with a reset button, btw. I keep one in my toolbox for troubleshooting.0 -
burnt transformers
Just wanted to thank everyone for the advice in diagnosing the transformer problem on a Weil-McClein hot water boiler, It was in fact the thermostat line going upstairs. Haven't pulled out the old wire yet, but temporarily moved the thermostat into the boiler room with new wire and it's working. The re-set transformer was a life-saver, I would have gone thru half a dozen more transformers had I not used the re-set type. This is going to stay in my toolbox.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements