new vaporstat+gauges+pigtail, ok to elevate / extend?
Options
Binnacle
Member Posts: 126
Just snagged a L608A (mercury switch, more accurate than J) Vaporstat and now am planning the install.
Ordered piping and gauges based on the 11/7/2012 2:23pm post by Rod to <a href="http://www.heatinghelp.com/forum-thread/143164/Noise-again">http://www.heatinghelp.com/forum-thread/143164/Noise-again</a> using the referenced PDF <a href="http://www.heatinghelp.com/files/posts/14911/Low%20Pressure%20Gauge%20Piping%20-%20%20Bill%20of%20Materials.pdf">http://www.heatinghelp.com/files/posts/14911/Low%20Pressure%20Gauge%20Piping%20-%20%20Bill%20of%20Materials.pdf</a>.
Is there an problem with adding a six-inch nipple plus coupling to extend the entire assembly so the Vaporstat and gauges are just above the top of the boiler housing?
-----
more details below, comments welcome!
skipping the bottom elbow nipple from the PDF and planning on attaching directly to the top of the LWCO
Substituted Wika 0-20oz low pressure and 30"Hg-0-30PSI liquid filled high pressure gauge, and planning to add a Ray Porous Snubber between the pigtail and 4-way cross fitting. Links:
<a href="http://www.valworx.com/product/low-pressure-gauge-25-0-20-ozsq-in">http://www.valworx.com/product/low-pressure-gauge-25-0-20-ozsq-in</a>
<a href="http://www.valworx.com/product/compound-gauge-25-30-hg-0-30psi-liquid-filled">http://www.valworx.com/product/compound-gauge-25-30-hg-0-30psi-liquid-filled</a>
<a href="http://www.valworx.com/product/ray-porous-snubber-14-npt-brass-a">http://www.valworx.com/product/ray-porous-snubber-14-npt-brass-a</a>
replacing the sight-glass too
Boiler is 1961 Weil McLain E-9-B, distant predecessor of the EG-65.
photo attached
Ordered piping and gauges based on the 11/7/2012 2:23pm post by Rod to <a href="http://www.heatinghelp.com/forum-thread/143164/Noise-again">http://www.heatinghelp.com/forum-thread/143164/Noise-again</a> using the referenced PDF <a href="http://www.heatinghelp.com/files/posts/14911/Low%20Pressure%20Gauge%20Piping%20-%20%20Bill%20of%20Materials.pdf">http://www.heatinghelp.com/files/posts/14911/Low%20Pressure%20Gauge%20Piping%20-%20%20Bill%20of%20Materials.pdf</a>.
Is there an problem with adding a six-inch nipple plus coupling to extend the entire assembly so the Vaporstat and gauges are just above the top of the boiler housing?
-----
more details below, comments welcome!
skipping the bottom elbow nipple from the PDF and planning on attaching directly to the top of the LWCO
Substituted Wika 0-20oz low pressure and 30"Hg-0-30PSI liquid filled high pressure gauge, and planning to add a Ray Porous Snubber between the pigtail and 4-way cross fitting. Links:
<a href="http://www.valworx.com/product/low-pressure-gauge-25-0-20-ozsq-in">http://www.valworx.com/product/low-pressure-gauge-25-0-20-ozsq-in</a>
<a href="http://www.valworx.com/product/compound-gauge-25-30-hg-0-30psi-liquid-filled">http://www.valworx.com/product/compound-gauge-25-30-hg-0-30psi-liquid-filled</a>
<a href="http://www.valworx.com/product/ray-porous-snubber-14-npt-brass-a">http://www.valworx.com/product/ray-porous-snubber-14-npt-brass-a</a>
replacing the sight-glass too
Boiler is 1961 Weil McLain E-9-B, distant predecessor of the EG-65.
photo attached
0
Comments
-
No problem at all
in fact, it's not a bad idea. Those things don't like to get wet, and extending it higher like that will help -- and won't make any difference in the pressure it senses.
Some folks say you don't have to fill the pigtail with water when you install it -- but I would recommend that you do. That will ensure that the equipment won't see steam either, and that always helps.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements