Combustion Testing
Options
TomS
Member Posts: 62
in Gas Heating
Tim, It seems that most manufacturers tell you to take combustion readings at full fire. Is there a reason for this? Lets say that you have a over sized mod con boiler and at max water temperature it is only firing at 50%. Wouldn't this be an appropriate level to take combustion readings? Thanks for any incite you can give me. Tom
0
Comments
-
No you should still over
ride and go to full high fire for proper adjustment and measurement. Some will have you do a hi fire and also a low fire test, do what ever the manufacturer ask for. This will insure lets say with a 5 to 1 turndown that all steps are properly set up.0