Gas fluctuation
Simply Rad
Member Posts: 192
in Gas Heating
Had a service call today for a Burnham power vented boiler. The boiler was moaning and groaning. I ran some tests and found that the inlet flowing gas pressure was fluctuating. The static pressure was 8" and the flowing was pulsing between 5.25"-7.3" THe outlet pressure was pulsing between 2.75-3.7" I checked the gas inlet into the valve and found no debre. When I tested the unit there was no other gas load. I then called the gas company to check the meter. I wasn't there when he showed up. He meet the homeowner and tested the meter and found no problems? Could the gas valve be bad and cause the gas supply to fluctuate? Thanks for your thoughts and happy holidays
Jeffrey
Jeffrey
Jeffrey Campbell
0
Comments
-
Was this a high pressure
system with a regulator at the meter or is it low pressure? It sounds like a low pressure system as you had a static pressure of 8" W.C. Was the fluctuation evident on any other equipment?
What is the make and number of the gas valve?0 -
gas pressure
The fact hat the pressure into the valve was fluctuating shows the problem on the supply side. The pressure drop on the inlet of a gas valve when the valve opens should not be more than 1/2" with 1" being the maximum when enough pressure is available. If the problem is not the meter then the piping is too small. Of course I have never seen piping change its size once installed. The fluctuation has to be from the meter.0 -
pressure readings
Sounds like water or some kind of liquid is somewhere either in the house piping or in the gas company piping. Any type of a dry blockage would show a lower operating pressure but it shouldn't fluctuate. A wet blockage would have your reading fluctuate. Have the gas company come back and have them take reading at the appliance, on the inlet and outlet of the meter and at the head of the gas service if its low pressure.0 -
How did you
make out?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements